The specific control valve is a Neles-Jamesbury G120S type (0.5 in) regulating hydrogen at low flows, i.e. 0-1.6 kg/hr. Based from the technical documents provided, upstream pressure is about 4300-4600 kPaa (from a header) and downstream pressure nearly 2500 kPaa. Average DP (based from actual data) is approximately 1900-2000 kPaa. Temperature is 30C.
Currently, the valve is erratic (scattered data points) - operates at 0-10% opening and registering flows of 1.7 kg/hr, even at 0%. I have looked onto the specifications of the valve, thinking that it might be oversized, but upon recomputation (utilizing Nelprof 5.0 - software provided by Metso, manufacturer of Neles-Jamesbury), it was actually undersized. The installed valve is using a spline trim #12, with Cv of 0.003, whereas the current demand should utilize a valve with Cv of 0.02. This corresponds to spline trim #7 or #8.
I'd like to ask how come that the data I have gathered shows that it is an "oversized valve" but in truth it was actually an undersized valve. What other factors could have contributed to such?
On a side note: We have another set-up identical to this one (we have two "plants"), and the same problem was encountered. The valve was replaced by a Fisher EZ globe control valve and an upstream orifice was installed. Data showed that good control was achieved, operation at 20-60% opening.
Thanks for all the help!