I am about to design an hazardous open drain system.The set-up is arranged in such a way that there will be drain box with overflow line to sea and drain collection line to a new open drain header will be routed to open drain caisson via seal pot.
Wondering how to size the overflow line from drain box.Shall i have to consider froude number (less than 0.3).But when i checked the NORSOK P-001,they mentioned that froude number is not to be taken into account.
I am wondering whether my understanding of standard is not right.Can anyone help me out.
NB!
Overflow capacity to be routed to sea is 45 m3/h.If I consider froude number,I will end up using 10" line.
Regards,
UKD