Commissioning New Line
#1
Posted 05 July 2010 - 02:06 PM
Can someone write the exact procedure to commission a new line servicing gas "mainly C1,C2" pressure 30 bar.
This gas is going to a compressor and we always have high delta P across the strainer of the suction of compressor
When we cleaned and removed the strainer we found it’s full of fine black powder, we continuously have this problem so we changed the
Strainer mesh size to larger holes
can someone write better approach to solve this problem other than changing the strainer mesh size?
what the possible source of this black powder ? could it be because the line is new?
#2
Posted 05 July 2010 - 03:53 PM
Gasco:
You obviously obtained the service of a bad piping contractor. You also failed to tie the contractor to a contractual agreement whereby the line would not be accepted until it produced a commissioned and clean operational run of at least several days on stream.
There is no telling what was left in the line after completion. Your company obviously inspected and accepted delivery of the line and paid for its full construction. It would be expected that you also pigged the line and ran it with a smart pig before accepting it.
All the issues being raised are issues that the owner assumes as his/her responsibility and, consequently, must take out insurance or invoke contractual terms to protect himself/herself. I have to assume this was done prior to letting the construction contract.
#3
Posted 05 July 2010 - 05:26 PM
Unfortunately this bad piping company supposed to be one of the largest construction company in the world
What we think the contractor did for commissioning the line is after the hydro test of the pipes that did not dry the line properly and after two years “because the project got delayed”. Dirt started forming in the line.
So what I am asking is there any way to solve this problem.
#4
Posted 05 July 2010 - 10:05 PM
Depending on what else is "wrong" or deficient with this pipeline, one way to attack the problem is to pig it. I would hire a pigging contractor and have the line analyzed after which the results of the findings could be evaluated and a decision made as to whether to clean out the line or to administer any suspected repairs.
After sitting idle without any drying or inert atmosphere, this line should be suspect and a thorough analysis would be in order, in my opinion.
#5
Posted 16 July 2010 - 12:50 PM
1) for preliminary cleaning :line flushing (if the line size is less than 10") or card-board blasting (if the line size more than 10" or cryogenic line)
2)Drying of line through plant air.
3) Since the line is going to Compressor suction, target test shall be conducted. Then depending on the number of spots found on the target plate, clearance to line can be given.
4)Leak test (testing each and every flange with soap solution, after pressuring the line at 5-6 kg/cm2g)
5)Then inertizing the line (since a hydrocarbon line) through nitrogen.
6)Ready for commissioning
But this can be done during a shut down.
PKS
#6
Posted 22 July 2010 - 03:02 AM
#7
Posted 22 July 2010 - 01:23 PM
#8
Posted 01 September 2010 - 01:05 PM
Your "Black powder" formation may be because of corrosion of iron with hydrogen sulfide (H2S) corrosion.
Corrosion products include black or blue-black iron sulfides, pyrite, greigite, mackinwaite, kansite, iron oxide (Fe3O4), magnetite, sulfur (S), and sulfur dioxide (SO2).
You may please check the feed for H2S concentration.
I don't agree with the idea of providing a larger mesh size strainer as it shifts the problem to a major area of concern, the compressor itself !
As far as other pre-commissioning steps are concerned,in addition to them i would like to do chemical cleaning of suction line and KOD rather more important in case of positive displacement compressor.
#9
Posted 03 September 2010 - 01:56 PM
Dear Himanshu,Sir,
I don't agree with the idea of providing a larger mesh size strainer as it shifts the problem to a major area of concern, the compressor itself !
Great Point to add at least for me.
#10
Posted 17 September 2010 - 08:03 PM
After period of time we stopped getting the black powder.
However, the suction strainer mesh have been removed completely along with the trip signal
"Previous trip signal of high delta P across the strainer was initially 0.8 bar then increased to 1.5 bar then after removing the mesh there is no trip value"
The decision of the removal was approved by the operation people and the compressor vender GE
just sharing you guys what happened later on
#11
Posted 22 September 2010 - 05:51 PM
#12
Posted 24 December 2010 - 10:17 AM
hi all
Can someone write the exact procedure to commission a new line servicing gas "mainly C1,C2" pressure 30 bar.
This gas is going to a compressor and we always have high delta P across the strainer of the suction of compressor
When we cleaned and removed the strainer we found it's full of fine black powder, we continuously have this problem so we changed the
Strainer mesh size to larger holes
can someone write better approach to solve this problem other than changing the strainer mesh size?
what the possible source of this black powder ? could it be because the line is new?
The root cause of your problem is like this:
After hydrotest, line was not properly drained, dried & purged.
Because of that, over period of time corrosion takes place & rust formation occured.
This rust was not even cleaned by pigging/card board blasting/blowing.
Solution:
To change the mesh size is not solution.
I would suggest first of all go for card bord blasting several times say 15 times depending upon volume of pipe & dust.
Then go for pigging say 5 ties.
Then go for chemical cleaning followed by mild passivation.
I can ensure you your proble will be solved forever.
Similar Topics
Ammonia Line Vapor GenerationStarted by Guest_simadri_* , 07 Apr 2025 |
|
![]() |
||
![]() Flow Through Normally No Flow LineStarted by Guest_iippure_* , 08 Apr 2025 |
|
![]() |
||
Inlet Line Not Free DrainingStarted by Guest_Asifdcet_* , 07 Apr 2025 |
|
![]() |
||
Improving Safety By Re-Routing Priming Vent Line In Centrifugal Pump HStarted by Guest_Srinivas Agastheeswaran_* , 31 Jan 2025 |
|
![]() |
||
Psv On Ko Drum With Flame Arrestor At Flare Vent LineStarted by Guest_Tintin2024_* , 29 Oct 2024 |
|
![]() |