We had an incident in one of our projects in which the vendor supplied a flare tip which was offerring a pressure drop of 1500 kpa against 15 Kpa which was the design parameter and guarunteed value. The design gas flow rate was 1400 ksm3/day gas. During actual plant operation it was observed that the back pressure value at flare stack bottom was 200 kpag at just 300 ksm3/day gas flow.
It was clear that the flare tip was incorrectly designed. However this was discovered a bit too late, in fact after 1 year of commisioning the flare tip. This has caught everyone by surprise as the plant integrity was doubted. During an emergency which requires the relief valves to operate, the relief header will be choked due to the high back pressure at the tip.
The tip pressure drop was confirmed to be less than 15 kpa all along the design phase and even now by the vendor. His supporting calculations are incorrect as we know now.
My querry to all of you is
1. Have you come across such gross errors in design by the flare vendor which can put the plant safety in jeopardy? How can this be found out and corrected in the design stage? (Apparently the pressure drop calculation is considered a propritery of the vendor and so is the tip design).
2. Are you aware of vendors who can carry out hydraulic capacity test (flow versus pressure drop) of the flare tips they are offering so that we do not end up with such difficultes?
Thanks and regards,
Benoy
Edited by benoyjohn, 05 September 2010 - 01:25 AM.