A question related to evaporative cooling. We have following air data:
Dry bulb temperature=131°F
Relative Humidity=60-90%
Atmospheric Pressure=14.43 psia
We want to cool a process stream to 105°F employing an air cooler. Keeping in view the ambient temperature, we can’t cool the process stream to 105°F unless we make use of evaporative cooing. Therefore, ewe contacted a renowned vendor dealing in evaporative coolers. He, the vendor, proposed that air under current set of conditions, air has a wet bulb temperature of 90°F. Hence, by using 15°F approach, we can easily achieve the required process temperature (105°F).
When I checked it with an online psychometric calculator (131°F dry bulb temperature is not available in most of psychometric charts available on internet), it gives following results.
With 60% RH, Wet Bulb temp=114.4°F
With 90% RH, Wet Bulb temp=127.05°F
Even with 60% RH, we can achieve a minimum of 114.4°F. Can anyone comment how the vendor is able to achieve 90°F wet bulb temperature?
Here is the online psychometric calculator i have used.
http://www.sugartech...ychro/index.php
Thanks All