Gravimeteric Feeders
#1 Heath007
Heath007
Posted 11 February 2011 - 04:57 AM
Good Evening,
I'm hoping someone with a coal feeder knowledge will be reading this thread.
I'm wanting to specify a gravimetric feeder...but I'm unsure on how to specify its feedrate...it would need to be variable type (of course)...is there a way of determining the feedrate (approximately) given the calorfic value of the fuel. I.e. 5800 kcal/kg and the size of my unit I.e. 660MW.
I could produce other data if needed.
Any comments would be greatly appreciated.
Thank you,
Justin Heath
#2 Mahesh@A&M
Mahesh@A&M
  • 80 posts
Posted 11 February 2011 - 04:55 PM
660MW is equivalent to 567497700 Kcal/hr. If coal moisture content is constant throughout, with 5800 kcal/kg calorific value, feed rate will 97.844 tons/hr.
If coal firing unit power has to be changed to different MW, input calculation in PLC and the output will become the new setpoint for weigh belt feeder.
I hope this is what you are looking for.
#3 Heath007
Heath007
Posted 11 February 2011 - 11:33 PM
Thank you ever so much Mahesh...I knew I was there somewhere, was just unsure of the math.
Thanks again.