Control Valve Bypass Size
Posted 28 September 2011 - 01:51 AM
I am trying to size a bypass valve for flow control valve. We received control valve sizes from vendor. But now how to decide the bypass size for that control valve?
Please guide for this problem
Thanks,
Venkatesh
Posted 28 September 2011 - 02:31 AM
Dear sir,
Thanks,
Venkatesh
Venkatesh,
Please at first refer to the relevant spec in your project. The criteria for necessity and selection of the by pass valve and its type/size would certainly be there. If you haven't any spec in this regard, please specify the valve size/type and other important information of the valve. With having those information i would suggest the proper by pass size for it.
Fallah
Edited by fallah, 28 September 2011 - 02:35 AM.
Posted 28 September 2011 - 02:46 AM
Control valve information-Flow control valve
6" Size
DP valve sizing=2.1Kg/cm2
Inlet pressure=4.6kg/cm2g
outlet pressure=2.5kg/cm2g
Inlet temp=40.3 C
Service=Sourgas
Flow in pipe=3413m3/hr
And also sir please provde information for calculation size,
Because we have other two control valves,we want to calculate bypass size for thos evalves also..
Posted 28 September 2011 - 04:10 AM
Sir,
6" Size
Inlet temp=40.3 C
Service=Sourgas
Venkatesh,
Seems you haven't any project spec regarding your qury. Well....
If your sevice is continuous, the control valve should be equipped with block valves and by pass. Sizes of block valves and by pass would be in accordance with API RP 550 and for mentioned control valve would be as follows:
-Sizes of block valves : 6" (if line diameter is 6") and 8" (if line diameter is 8").
-Size of by pass valve : 6" (for line diameter of 6" and 8").
For other valves, please refer to mentioned RP.
Fallah
Edited by fallah, 28 September 2011 - 04:12 AM.
Posted 28 September 2011 - 05:00 AM
Tahnk u so much for fast reply for my query .
Sir i'm attaching my control valve aseembly which is suggested by my lead.Plz check and guoded me if any corrections
Posted 28 September 2011 - 05:40 AM
venkatesh,
Supposed you mean case-1 of the attachment, if so please finf below my comments about the configuration and its detail:
- Sizes of the block valves should be 10" instead of 12" to meet the API RP 550 requirement.
- Because mentioned flow control valve is used as SDV, the valve along its by pass (size 10") should be specified as CSC (Car Sealed Closed).
Fallah
Posted 28 September 2011 - 06:02 AM
Sir can u attach API 550 ,We don't have that standard,that is very useful for me
Your prompt reply is awaited
Posted 28 September 2011 - 06:27 AM
Venkatesh,
Sorry, it is not permitted and you can buy it or ask from your company to provide.
Fallah
Posted 28 September 2011 - 07:00 AM
#10
Posted 28 September 2011 - 12:37 PM
Your PID shows the control valve also having a shutdown function. This is considered bad practice, especially on a fuel gas line. Every client I have worked for would require a separate ESD valve in the line.
Consider the following emergency scenarios:
(1) The control valve fails to operate correctly, leading to a fire at the unit being fed by the fuel gas. How do you shut the plant down safely?
(2) The control valve is offline and you are running on the manual bypass. There is a fire (anywhere on the plant). How do you shut down the fuel gas safely while allowing the operators to escape?
These hazards and others would come to light if a HAZOP review is carried out.
Paul
#11
Posted 29 September 2011 - 11:12 AM
seated equal percentage valve would be needed to obtain a Cv between 100 and 200% of that of the control valve, as called for in the International Practices. For a gate valve two sizes smaller than that of the control valve would be needed to meet these criteria. Gate and globe valve Cv values are not well known and it is doubtful that a contractor would select sizes in accordance with the International Practices unless the criteria were specifically brought to his attention.
For situations in which a flow rate many times normal is needed for occasions such as filling a unit, a larger than normal or perhaps a second bypass valve may need to be specified. Conversely, as pointed out under “Choice of Failure Position,” for control valves, there may be situations that justify putting an upper limit on the bypass valve capacity.
#12
Posted 29 September 2011 - 10:09 PM
As Steven7788 has clearly indicated, size of bypass valve depends on the function that you require from it; this function can be different from valve to valve. There are general criteria, yet I think the intended function is predominant for the design.
I also agree with paulhorth, control and ESD functions should be implemented by independent instrumentation for safety. I have only heard discussions in case of a boiler, whether their corresponding PLCs could be combined (answer not known by me).
(*) Instrument Dept often selects one size smaller bypass diameter, especially for big diameters ( to some practices). For the specific case same diameter was judged proper by Process.
Correcting note, 1 Oct 2011: PLCs of ESD and startup to be combined, if codes permit, not ESD and general control functions.
Edited by kkala, 01 October 2011 - 01:06 AM.
#13
Posted 30 September 2011 - 03:47 AM
1. If we understand the purpose of having the bypass line for control valve, we should not have any problem in determining the size of bypass valve. Having said that, my review of your two cases, bypass valve is over-sized.
2. ESD as an integral part of basic control system is an old design which is no longer acceptable by current practice of process safety. Please refer and study the attached diagram for basic understanding of the system. The first scheme (BPCS) is considered as a single layer of protection (higher risk). The second diagram (SIS) os a two layer of protection and hence increase the safety integrated level (SIL).
Edited by S.AHMAD, 30 September 2011 - 04:02 AM.
#14
Posted 01 October 2011 - 12:58 AM
According to concept of independent ESD from control actions, THSD would close only EBV. If it was considered necessary for FC valve to close from high temperature (and this is extra safety), it would be realized through another control action, e.g. through a separate THSD.
A recent boiler process duty spec (2008, boiler now made by Vendor) required this independence between control and "ESD / startup" functions. On the other hand technology progress may have made "mixing" of control and ESD functions reliable enough in some cases.
Edited by kkala, 01 October 2011 - 12:59 AM.
#15
Posted 01 October 2011 - 04:34 AM
Ahmed sir
Can you provide any theory for SIS.pdf so that i can understand more clearly because i'm fresh process engineer.
#16
Posted 02 October 2011 - 02:56 AM
Editing Note: Found http://library.abb.com/global/scot/scot211.nsf/veritydisplay/5c62194fa3f47c2dc1256ed70030f1b0/$File/3KDE010001R5001.pdf could give some insight.
Edited by kkala, 02 October 2011 - 03:07 AM.
#17
Posted 02 October 2011 - 07:55 PM
You can also get the details from following standards:
1. ANSI/ISA-84.01-1966: Applications of Safety Instrumented Systems for the process Industries
2. ANSI/ISA-84.00.01-2004 (3 Parts)
3. Technical Report: ANSI/ISA-84.00.02-2004 (5 Parts)
For an introduction, please find attached a copy of presentation slides that I normally used to introduce the subjects to participants of HAZOPS Training Workshop that I frequently conduct.
In the slide: PFD = Probability of Failure on Demand
Hope the above info helps.
Edited by S.AHMAD, 02 October 2011 - 08:27 PM.
#18
Posted 03 October 2011 - 06:32 AM
#19
Posted 03 October 2011 - 07:00 AM
Wasn't it better a new thread been opened with the subject of SIS, ESD,....,or something like it....?
Edited by fallah, 03 October 2011 - 07:07 AM.
#20
Posted 13 November 2011 - 07:25 PM
In a locally designed condensate treatment unit, any case of (steam) bypass valve was specified as having same Cv (flow coefficient at fully open valve) to that of the control valve; this on the ground that there will be manual control through bypass in case that control valve is removed for maintenance. In that sense bypass piping was of same diameter as main piping (*). Downstream PSV flow was specified for fully open control valve plus half open bypass valve (1.5Cv in total), in other cases both valves are conservatively considered fully opened (2Cv). Check & necessary revisions according to real Cvs from supplier (it could be one for both valves, to my information) is realized during detail engineering. This practice for bypass valves was often applied in my working environment .
Dear fallah,
For PSV calculation of control valve failure, why downstream PSV flow should plus half open by pass valve(1.5Cv in total), in other cases both valves are conservatively considered fully opened (2Cv)?
thanks
Jia Tong
#21
Posted 13 November 2011 - 11:36 PM
There is a standard chart in EIL engineering guidlines with respect to control valve, block valve & bypass valve size is defined. This is thumb rule no need to go for any calculation.
Generally for the lower size of control valve around 3 " bypass valve size shall be same as control valve size & above that one size lower. Please follow standard table.
Jatin
#22
Posted 14 November 2011 - 01:56 AM
Dear fallah,
thanks
Jia Tong
Jia Tong,
Attached from API 521 included the response to your query. If you need additional assistance inform me to provide.
Fallah
Edited by fallah, 14 November 2011 - 01:58 AM.
#23
Posted 14 November 2011 - 06:17 AM
Attachment by Fallah speaks of two cases, as examples:Jia Tong, Attached from API 521 included the response to your query. If you need additional assistance inform me to provide. Fallah
Dear fallah, For PSV calculation of control valve failure, why downstream PSV flow should plus half open by pass valve(1.5Cv in total), in other cases both valves are conservatively considered fully opened (2Cv)? thanksJia Tong
(1). When bypass valve is partially opened during operation to "assist" the control valve.
(2). When bypass valve operates instead of the control valve, removed for maintenance.
Case (1) could conservatively correspond to 2Cv, while case (2) to 1.5Cv. It is noted that Cv of control and bypass valve was considered same in the post of 30 Sep 11, where 1.5Cv & 2Cv was mentioned.
API can differ somehow to presented local practices, the latter being simplified and (in this case) more conservative.
Edited by kkala, 14 November 2011 - 06:24 AM.
#24
Posted 15 November 2011 - 01:40 AM
Dear fallah,
thanks
Jia Tong
Jia Tong,
Fallah
dear fallah,
Thank U so much. This is a big help for a fresh engineer like me.
Another question: in the all normal cases, I can calculate and seek out the corresponding Cv of control valve. The vendor of control valve can confirm its final size according to these Cv. For case of control valve failure, when calculate relieving flow of PSV, we should use the Cv of fully open control valve. But some time, this value is too great and accordingly, the relieving flow is too great. For this problem, I find some one use the double Cv of the normal case as the the Cv of fully open control valve to calculate the relieving rate. Is this method right? in the all normal cases, I can calculate and seek out the corresponding Cv of control valve. The vendor of control valve can confirm its final size according to these Cv. For case of control valve failure, when calculate relieving flow of PSV, we should use the Cv of fully open control valve. But some time, this value is too great and accordingly, the relieving flow is too great. For this problem, I find some one use the double Cv of the normal case as the the Cv of fully open control valve to calculate the relieving rate. Is this method right? in the all normal cases, I can calculate and seek out the corresponding Cv of control valve. The vendor of control valve can confirm its final size according to these Cv. For case of control valve failure, when calculate relieving flow of PSV, we should use the Cv of fully open control valve. But some time, this value is too great and accordingly, the relieving flow is too great. For this problem, I find some one use the double Cv of the normal case as the the Cv of fully open control valve to calculate the relieving rate. Is this method right? whether this method is related to the selective principle of the Cv value?
dear kkala,
thanks for your reply.
For case (2) you said, 1.5 Cv is more more conservative.1 Cv is just ok as API 521. Is my opinion right?
For some project, their manual valve in the by pass line is lock-closed and so they don’t consider the double relieving rate. For this measure, how do you think that?
regards,
Jia Tong
Edited by dwwjt812, 15 November 2011 - 02:08 AM.
#25
Posted 15 November 2011 - 06:34 AM
dear kkala, thanks for your reply.
For some project, their manual valve in the by pass line is lock-closed and so they don’t consider the double relieving rate. For this measure, how do you think that? regards, Jia Tong
A correction on my previous post: Presented local practices (realized) are simplified but not generally more conservative compared to API. See "API_STD_521-Control Valve Failure.pdf", next paragraph to the one placed in red square.
- Case (2), bypass valve operating, when control valve is at maintenance: API says that you can base relieving capacity on single Cv (maximum of the two), on the condition that bypass valve is locked close (administrative control) during normal operation.
Also that only "locked close valve" may not be reliable, if inadvertent opening of bypass valve can cause overpressure exceeding hydrostatic test pressure (corrected, I assume for temperature) somewhere downstream, likely to cause a catastrophic accident .
Note: I have not seen this last clause applied, advice / examples by others would be welcomed. Risk assessment during hazop may be needed.
- Locked closed bypass valve, while control valve is operating: Same case as before.
Hope it helps, representing my understanding.
Edited by kkala, 15 November 2011 - 06:42 AM.