To the useful posts already sent, I woud like to add points as below.
A. Local refineries do not to use VSDs in general. Asking why, the answer was "because of the hazardous areas". Search on the web indicates following.
A1. A VSD motor releases more heat than a normal motor, so it requires special provisions to be suitable in hazardous areas. See
http://www.reliance....notes/d7736.pdf, VFD (variable frequency drive) is another name for VSD.
A2. For motors operating in hazardous areas, their VSDs are located far from them, in "clean areas", e.g. in control rooms (or with motor control centers, I assume). Recently it has been possible to install VSDs in hazardous areas. See above web reference, as well as
http://www.todaysfac...ouse-hinds.html.
A3. So there are VSD motors suitable for hazardous areas, their extra cost impact has to be assessed.
B1. In an alumina project in the past (1993) a lot of VFD drives were purchased, with max rotational range about 2 : 1. Modern VFDs are smaller in size and of higher range, apparently satisfying requirements by ing80. See
http://www.practical...m-range-222075/, even though they concern a lathe.
Note: Pump affinity laws are not precise for such a broad range. See http://www.eng-tips....=198102&page=23. Better to specify low and high requirements (flow, head, etc) for the VSD pump and let vendor define RPM range (if this option is selected).B2. What if the installed VSD pump needs maintenance? You may need another pump as standby.
C. Probably a way out is to clarify the two options, constant speed pumps or VSD pump(s), estimate their capital and operating cost, tabulate their data and have the decision.
Note: Constant speed pumps might be a simpler, yet more expensive solution (personal opinion). Note on 4 Oct 2011: Again seeing why local refineries do not install VFDs , I understood they are reluctant due to lack of experience, mainly on maintenance. Have VFDs been adopted in other refineries?This may seem too conservative, however I remember 3 years of fruitless effort to calibrate H2SO4 flow into a phosphoric acid plant, when a "modern" control system was installed (1977-80). The old "primitive" system operated satisfactorily, smoothed by long wide application.