Light Diesel Oil Tank
#1
Posted 12 January 2012 - 12:16 AM
For light diesel oil tanks, is it necessary to have heater within tank to keer temp up ?? kindly suggest
For firing into burner, what type of atomizing media will be used, i think this should be compressed air but dont know why, kindly suggest.can steam will be used
Looking forwrd for propmt reponse
Thanks
#2
Posted 12 January 2012 - 10:52 AM
It is noted also that flash point of local diesel is 55 oC, so heating can exceed this temperature, creating risk of fire.
Fon standby boiler burners (the boilers normally burn fuel oil) we use compressed air as atomizing medium. See http://www.cheresour...tomizing-steam/. Steam atomization for diesel is met in refineries, but is not so efficient as compressed air. As Nelson understood to say, gas oils and distillate fuels (except naphtha) are not easily atomized through steam, unless mixed with residual fuels (Petroleum refinery engineering, 4th edition 1958, p. 425, the burning of oil fuels).
#3
Posted 23 January 2012 - 09:29 AM
Let us begin by the fundamental principle of Fuel oil burning
- The oil must be vaporized, since all combustible matter must be converted to a vapor or gas before combustion can take place. This is usually accomplished by the application of heat.
- The oil vapor must be mixed with air in order to have oxygen present for combustion.
- The temperature of the mixture must be increased above the ignition temperature.
- A continuous supply of air and fuel must be provided for continuous combustion.
- The products of combustion must be removed from the combustion chamber.
of nozzles, this energy is supplied in the form of pressure ,having said the same ,MP steam pressure level ensures that fuel oil is properly 'atomized' for combustion,air header pressure is normally lower than MP steam so atomization may not be as good as achieved by MP steam.
Other thing is that oil preheats to a certain extent (closer to ignition temp) while being atomized by MP steam ,this is not possible with air that is usually at ambient conditions.
Steam as an atomizing media also helps down to cut down visible soot or carbon black form the flame.(remember shift reaction !)
I am open to hear the arguments in favor of air as atomizing media, may be i can utilize the wisdom gathered in my next refinery design !
I have seen Diesel tanks with steam coils and i consider them a foolish design practice as pointed out by Mr.Kkala.The only argument operation personnel make out is haziness of diesel while temp drops down too much,water dissolved in diesel separates out and give diesel a hazy appearance.This they deal with a slight heating with steam coil though its a risky operation while flash point is 55to 66 Deg C.
Diesel haziness can be dealt with a properly designed diesel coalescer rather than operating dangerously !
#4
Posted 24 January 2012 - 06:37 PM
-Referred Nelson relates atomizing to foaming. Fuel oil and steam are mixed up in the burner, resulting foam bursts into a fine mist when coming out of the tip.
Residual fuels have better atomizing or foaming properties. Gas oils or distillate fuels do not atomize easily unless mixed with residual fuels (but naphtha can be burnt satisfactorily through a suitable burner tip) (Nelson, loc cit, post No 2).
2. For the two refineries around Athens, we have not designed diesel oil tanks with heating coil (this was confirmed). No such a case have been heard of (at least by me) concerning diesel tanks in other refineries.
Edited by kkala, 24 January 2012 - 06:47 PM.
#5
Posted 24 January 2012 - 09:28 PM
#6
Posted 26 January 2012 - 01:09 PM
As said, diesel tank heating seems not to be locally applied. Specs for diesel, probably related to it, call for:
Automotive diesel : Cold filter plugging point (CFPP) max: -5 oC (winter), +5 oC (summer)
Heating diesel: CFPP max : -5 oC (winter), no requirement (summer)
Pour point, max: -9 oC (winter), 0 oC (summer)
Edited by kkala, 26 January 2012 - 01:13 PM.
#7
Posted 26 January 2012 - 07:07 PM
#8
Posted 27 January 2012 - 04:24 AM
It will ne very helpful if you guide me about what minumum distance to be maintained away from diesel tank so that another equipment to be placed and also to make boundary around LDO tank,what are noraml practice regrding these.Your kind input is required on above.thanks
Looking for prompt response.
#9
Posted 27 January 2012 - 11:31 AM
Steam feeding valve can be controlled by liquid temperature (but if it fails?). High temperature switch can interupt steam supply when liquid temperature gets close to 55 oC, with high temperature alarm before.
So what are the necessary measures and conditions (such as those supposed above) during diesel oil tank heating, actually applied in practice?
Relative risks are more or less presented above.
Edited by kkala, 27 January 2012 - 11:38 AM.
#10
Posted 27 January 2012 - 12:19 PM
You can look, as an example, into http://www.npchse.ne...PS/C-sf-550.pdf '> http://www.npchse.ne...PS/C-sf-550.pdf , appendix A, Tables A.5 and A.6. General trend for safety distances can be generally (not for a diesel tank) seen at http://www.cheresour...-storage-tank/'> http://www.cheresources.com/invision/topic/13803-propane-storage-tank/. Nevertheless local refineries are not understood to apply safety studies yet for the distances between atmospheric storage tanks.It will ne very helpful if you guide me about what minumum distance to be maintained away from diesel tank so that another equipment to be placed and also to make boundary around LDO tank,what are noraml practice regrding these.Your kind input is required on above.thanks.
#11
Posted 30 January 2012 - 10:36 PM
#12
Posted 01 February 2012 - 06:22 AM
Thanks
#13
Posted 01 February 2012 - 06:46 AM
Consider this resource or try to find a copy of NFPA 30
http://www.epa.gov/o...vkinpresent.pdf
Hope this helps
Breizh
#14
Posted 01 February 2012 - 10:22 PM
Thanks
#15
Posted 01 February 2012 - 10:27 PM
there is an example
Edited by breizh, 02 February 2012 - 01:47 AM.
#16
Posted 15 April 2012 - 09:46 PM
what s the diffrence between heavy fuel & light fiuel???
is there any diffrence in thier storage tanks??
BR,
#17
Posted 16 April 2012 - 02:11 AM
2. Storage may or may not be the same. However, light F.O can be stored in heavy F.O tanks but heavy F.O may not be stored in light F.O tanks. It depends on the properties specifically the pour point and viscosity.
3. Any oil having pour point of higher than ambient, must have heating system for ease of pumping. Most heavy F.O tanks is equipped with heating system.
Edited by S.AHMAD, 16 April 2012 - 02:12 AM.
#18
Posted 16 April 2012 - 03:06 AM
could you tell me about thier heating system??
is it a heater inside of tank???
does it need to any special insulation???
#19
Posted 16 April 2012 - 03:25 AM
could you tell me about thier heating system??
is it a heater inside of tank???
Hyper,
The heating system normally is steam coil.
Fallah
#20
Posted 16 April 2012 - 03:33 AM
2. As mentioned by Fallah, steam coils has been the popular method but do not restrict your mind, explore alternatives.
3. All piping surface of higher than 60C must be insulated for personnel safety and/or for energy saving. Steam traced is normally provided if pour point is high.
Edited by S.AHMAD, 16 April 2012 - 03:33 AM.
#21
Posted 16 April 2012 - 04:50 AM
first i should be appriciated for your kind replies.
Mr. Ahmad, please be informed that i want to know about storage tank not pipeline.
for tank insulation(for prevent loss of heat-pour point is high for HF), Which methode is common????
#22
Posted 16 April 2012 - 09:08 PM
2. No specific method for insulation
Edited by S.AHMAD, 16 April 2012 - 09:09 PM.
Similar Topics
![]() Phosphoric Acid 56% Tank LiningStarted by Guest_Phosphoric123_* , 20 Apr 2025 |
|
![]() |
||
![]() Tank Inlet Diffuser LengthStarted by Guest_RAFAELDAVE_0752_* , 08 Apr 2025 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |
||
Tank Filing TimeStarted by Guest_not_mikhail_* , 17 Mar 2025 |
|
![]() |
||
Off Spec Condensate Storage TankStarted by Guest_shekhar dhuri_* , 05 Sep 2013 |
|
![]()
|