1. The problem posted by Rohollah is not with the "control valve" but it is the piping downstream P3. Cavitation may occur at the control valve BUT that is not the problem
2. As long as the temperature is above 113C (sat temperature at 0.6 barG), flashing will occur. That is why cooling the stream below 100C will be the permanent solution. That is by eliminating the root cause (temperature higher than sat temp)
3. It is VERY obvious that the problem is associated with two phase flow.
4. At the pressure of 0.6 barG, 1 m3 of water turns into steam of 1091m3. This means that the velocity increases by 1000 times. Let say as per DBShah that the flashed steam is only 5%, that mean the velocity increases by 50 times for every 1 m3 of water flashes.
5. If the current velocity is 1.5 m/s then the average velocity will be 75 m/s. It is even worst if the current velocity is 3 m/s (150 m/s). The normal practice is to keep below 45 m/s for steam. The recommended velocity should be even lower for two phase flow and if the waste water is acidic.
6. The actual velocity is expected higher than 50 times since the cross sectional area available for the steam is much smaller than the pipe cross sectional area that is mostly occupied by water.
7. If cooling the stream is not viable, then the next best solution is to size the drain pipe correctly.
8. The solution should be simple but cost effective.