I have a question regarding the calculation of percent pressure drop (%dP) for the 3% rule/guideline for relief system inlet piping pressure drop per API / ASME. I found this post from a few years ago that is directly related to my question, but it doesn't seem to me that the thread came to any definitive answer, so I am posting the question again.
My question is, after you calculate your inlet piping pressure drop, do you divide that by the set pressure in gage units or absolute units to get the %dP for comparison with the 3% rule?
For certain applications, this could mean the difference between meeting the 3% pressure drop requirement and not. I realize this 3% requirement is not mandatory, and one can use the manufacturers recommendations. But, for all intents and purposes of this post, let's assume it is a mandatory requirement.
So, for example, let's say I have a relief system with a set pressure of 75 psig and I have calculated the pressure drop across the inlet piping to be 2.5 psi. Then we would have the following calculations, one with gage units and the other with absolute units:
Pset = 75 psig = 89.7 psia
dP = 2.5 psi
1. %dP = (dP / Pset) * 100 = (2.5 psi / 75 psig) * 100 = 3.33%
2. %dP = (dP / Pset) * 100 = (2.5 psi / 89.7 psia) * 100 = 2.79%
Now, engineering judgement would tell me that the more conservative case would prevail, i.e. I should use the set pressure in gage units since it will always be smaller than absolute units and therefore yield a higher %dP.
However, I would like to know what standard industry practice is for these calculations, and what the good people of cheresources practice.
Summary Questions:
To calculate percent pressure drop for comparison with the 3% rule per API / ASME, does one use the set pressure in gage units or absolute units?
What is the standard industry practice for calculating percent pressure drop with regards to the above question?