Determining The Set Point Of Trvs


This topic has been archived. This means that you cannot reply to this topic.
5 replies to this topic
Share this topic:
| More

#1 CHEMeng88

CHEMeng88

    Junior Member

  • Members
  • 10 posts

Posted 14 October 2012 - 08:41 AM

Hi,

i need some help on cascading TRVs..

1) TRV-1 is protecting a line (design pressure = 200psig). So the set point for TRV-1 is set at 200psig
2) TRV-1 pops into a line (design pressure = 150 psig). TRV-2 is present to protect this line. TRV-2 then pops into a closed system with backpressure of 10psig

Question:

How do I determine the set pressure of TRV-2?

Thanks!

#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,016 posts

Posted 15 October 2012 - 04:00 AM

CHEMeng88,

You did fail to submit the operating pressure of each line and type of the TRV's. Anyway, considering line design pressure/back pressure, appears the second line could be protected by a conventional TRV with a set pressure equal to 150 psig.

Fallah

#3 S.AHMAD

S.AHMAD

    Gold Member

  • ChE Plus Subscriber
  • 786 posts

Posted 30 October 2012 - 02:38 AM

1. Spring differential pressure TRV-1 = 50 psi (i.e. set presure = 50 psig)
2. Spring differential pressure TRV-2 = 140 psi (i.e set pressure 140 psig)
3. so the total set pressure 50+140+10 = 200 psig.
4. therefore, you can also select any combination of set pressure such that TRV-1 + TRV-2 +10 = 200 psig such as 100+90+10 or 90+100+10 = 200 psig etc. and TRV-2 + 10 must not exceed 150 psig
5. Such arrangement is sometime known as piggy-back arrangement

Edited by S.AHMAD, 30 October 2012 - 02:41 AM.


#4 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,016 posts

Posted 30 October 2012 - 08:13 AM

CHEMeng88,

Considering economical issues to reduce the TRV's sizes by using design pressure potential, it might the optimum set pressure and type for TRV-1 and TRV-2 be as follows:

TRV-2 with set pressure equal to 100 psig and conventional type; provided that the superimposed back presure (10 psig) is the maximum value of the BP (maximum 10% of the set pressure)

TRV-1 with set presure equal to 200 psig and pilot operated type (can tolerate high back pressure of 50% of the set pressure and keeping the stability)

Fallah

Edited by fallah, 30 October 2012 - 08:13 AM.


#5 S.AHMAD

S.AHMAD

    Gold Member

  • ChE Plus Subscriber
  • 786 posts

Posted 30 October 2012 - 09:24 PM

Fallah/CHEMeng88,
1. As far as I know, TRV are spring loaded of 3/4" normally more than adequate.
2. What important is the spring differential pressure.
3. If pipe-1 design pressure 200 psig and protected by TRV-1 set at 200 psig (spring differential pressure 200 psi), when a both TRVs popped, pipe-1 relieving pressure will be 200+150 or 350 psig since the discharge of TRV-1 has a back pressure of 150 psig. Similarly for pipe-2 the spring differential must be smaller than 140 psi since the TRV-2 is discharged to 10 psig back pressure.
4. Therefore we must very careful to ensure the pipelines are protected accordingly. Set pressure if tested against atmospheric pressure will be equal to spring differential pressure.
5.If we specified TRV-1 set to be 200 psig, the spring differential must be set at 50 psig if TRV-2 is set at 150 psig with spring pressure of 140 psi.
6. My suggestion to set spring pressure for both TRV to be 95 psig. So that when both TRVs popped, Pipe-1 and pipe-2 will be exposed to 200 psig and 105 psig respectively.
7. . I hope my brief explanation is clear enough to avoid confusion. I have done several designs of this type of arrangement before.

Edited by S.AHMAD, 30 October 2012 - 09:35 PM.


#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,016 posts

Posted 31 October 2012 - 02:01 AM

AHMAD,

The configuration submitted by CHEMeng88 is named Daisy Chaining TRV's and to be executed by chaining the TRV’s at higher set pressures into piping operated at lower pressures. These configurations, as i mentioned, need pilot operated TRV's due to high and variable back pressures. Then i repeat my suggestion submitted in my post No. 4 as set pressures of TRV-1 and TRV-2.

Fallah

Edited by fallah, 31 October 2012 - 04:12 AM.