1. Article attached to post No 18 (by breizh) has been also referred in
http://www.cheresources.com/invision/topic/14826-criteria-for-the-usage-of-vortex-breakers-in-drums.
Article attached to post No 10 (by katmar) explains how ambient air intrusion was eliminated in a rectangular basin, also noting that major modifications on it can be cost prohibitive.
Just to complete this matter a bit, basin as per attached "
CT.xls" did not develop air intrusion or pockets in suction / discharge piping (it depends on operating parameters too), yet its horizontal CW pump was hard to prime.
Link in post No 8 (by ElSid) is a useful article, attached as "
CTnoise.doc" here, since a lot of links are not valid after some time.
2. Nevertheless post No 4 (by GTE) and CTnoise.doc indicate excessive cooling water aeration as (main) cause of noise in the pump (non classical cavitation) and of air lock in downstream plate heat exchanger. This can be verified by throttling pump discharge. Potential remedies mentioned in CTnoise.doc could be:
α. Small quantity of air injected into suction line; but this would increase air pockets in the exchanger.
β. Increase suction diameter to result in 3 ft/s (maximum), make it "smooth", slope it so that formed air bubbles escape to the surface of the basin (post No 12 by ElSid). Depending on suction line, this may be easy or not; extent of success is not known in advance.
3. The "floating plane" mentioned in recent posts may hit the target, yet extent of success is not known either. It is understood as a floating plastic surface (without depth). Falling water bounces on it, then flows along it to all horizontal directions into the basin. Splashing is anticipated. Channeling of horizontal flow might occur.
It may be useful to measure air content of cooling water (*) to check assumption of excessive aeration. Even better, use a small "floating plane" as a pilot for experiments.
(*)
Fill a lab bottle with "aerated" cooling water and place a rubber cap on it. Shake and keep at constant low temperature (thermostat). 4% v/v air will make a difference over water vapor pressure of a blind sample in an identical bottle. This is just an thought, there may be better ways to measure air content.A "floating pan" with internal baffles may be more efficient, but quite complicated.4. Irrespectively of the above, it may be worth while looking into following.
(α) Place the end of suction line far from the visible place of air bubbles in the basin..(β) Place automatic air vent on plate heat exchanger (like that on house radiators) or just upsteam of it, to mitigate air lock. Experienced opinion on it is welcomed.
Edited by kkala, 30 December 2012 - 09:48 AM.