A brief search seems to suggest that such basin should not be located below the pressurized storage but at some distance according to API 2510A (edition of 1996 found), probably 100 ft far. In this way chance of flame impinging on the vessel is minimized in case of fire; otherwise you risk vessel explosion, in case that rupture has not completely emptied it. HAZOP and mainly safety study can assess and clarify such matters.
Previous posts accept creation of liquified gas pool as possible (*). The question posed is whether design shall try to contain this pool. Is there any alternative measure? The event seems credible, despite all preventive measures (safe mechanical design, firefighting, distances, etc), which of course should be implemented. Let us see results of mentioned brief search. It is noted that query has asked for (statuary) regulations on liquefied gases storage in various countries.
1. Mentioned Greek legislation in post no 2 deals also with low pressure refrigerated LPG storage (LPRS), requiring basin around the tank. Basin must be able to contain 75% of tank capacity if there is one tank (100% of biggest tank in case of up to 3 LPRSes). This differs to pressurized storage; but indicates containment of liquid LPG spillage, being same in temperature and composition as the pool above.
2. "Process-Safety-Considerations-Design-LPG-Pressure-Storage-Vessels.pdf" (from Web), probably reflecting Saudi Aramco's practice, "Impounding Basin / Diking / Catchment Requirements".
Ground is sloped, leakage is collected in impounding basin at some distance.
3. "Std-118SEP2004.doc" (from Web), Chapter 8.0 "Layout of LPG facilities", 8.1.1 "LPG storage".
Spheres and bullets shall be treated as separate groups; LPG storage vessels shall not be located in same dikes with other stored liquid hydrocarbons.
Spillage collection shallow sump shall be located at a distance where the flames from sump fire will not impinge on the vessel. This distance shall not be less than the diameter of the nearest vessel or 15 meters, whichever is higher.
4. LP Gas Association's "LPGA CoP 1 Bulk LPG storage at fixed installations, Part 1: Design, installation and operation of vessels located above ground" (Jul 1998), found in HSE (UK) web site, can be useful but is not free. Its relevant recommendation from somebody having access would be welcomed.
5. API 2510A (2nd ed, Dec 1996) referring to pressurized LPG vessels, para 2.4 "Drainage and Spill Containment".
-Objectives are to prevent accumulation of liquid under LPG vessel, provide a location for accumulating liquid to minimize risk (if fire occurs) on critical nearby equipment, confine spillage to smallest practical area to reduce vapor cloud size.
- Reference to API standard 2510 is made, para 3.2-3.5, for spill containment requirements. Even though high-vapor pressure LPG may not form a pool when released, the principles of good drainage should nevertheless be considered.
- Impoundment area (IA) may be either inside or outside of a dike surrounding the vessel storage area.
- Liquid capacity of IA shall be per API 2510 (para 3.2.3.4 or 3.2.4.3). IA should be located at a distance necessary to minimize chance of flame impinging on a vessel, which requires an engineering analysis. There is little risk for distances of about 100 ft, or more.
-Following para 2.5 "Ignition Source Control": All ignition sources must be recognized, identified and restricted to safe (nonhazardous) areas, or contained safe locations.
I think it is worthy to get latest editions of API 2510 and API 2510A. These make the most complete source out of those seen, contain more than what reported here, could contribute to safer design.
(*) Suppose ambient temperature=10 oC and stored C4H10 going out through a rather big rupture in liquid and vapor phase. 6.1% of liquid C4H10 will be vaporized and this will also entrain liquid droplets in the created mist. When vessel gets atmospheric pressure, remaining liquid C4H10 (0 oC) will flow by gravity. Flashing will not be violent since heat transfer from environment will be rather slow. Not having seen such event, it is supposed to occur so. Behaviour of butadiene is expected similar (similar normal boiling point = -4.4 oC).
Edited by kkala, 15 February 2013 - 11:38 AM.