The problem what I perceived is more than effective method of chemical cleaning. Additionally, basic relevant data which is required to pin point the problem is missing. I have observed that people are reluctant to provide necessary data on forum which might help other experienced people to give relevant comment and share their experience. This to some extent reduces the effectiveness of the forum
I am giving you a detailed reply with some suggestion and assuming that you will keep all the members posted on the forum the result and remedy of your issue
Let starts with the basics
Sea water is used as heat sink by three possible routes
- Direct Use of Sea Water
- The seawater is pumped directly to the heat exchanger and there is direct transfer of heat from the hot medium being cooled to the seawater
- Indirect Use of Seawater
- Heat is exchanged between the seawater and a secondary stream which could be fresh water; or a mixture of fresh water and, or , glycol. This secondary stream is then used as cooling medium. In general, for offshore use, water with typically 30% of tri-ethylene glycol (TEG) or mono-ethylene glycol (MEG) is used as the secondary cooling medium. For onshore use, fresh water is often used if climate conditions permit.
- Use of Seawater in Cooling Towers
- In some areas, it may be economical to utilize seawater in cooling towers. In this case the heat rejection is not only to the sea but also to the atmosphere due to partial evaporation of the seawater. This obviously can make available an alternative source of cooling tower water where fresh water is expensive. It can also lead to a considerable reduction of pumping power and thermal pollution
- Usually, in such systems, the seawater is cycled through the cooling tower for no more than two cycles, to minimize corrosion and fouling. For fresh water is concentration cycle usually varies between 3-5 depending on the chemistry of water and metallurgy of the downstream plant
Needless to say, the information that what type of above system in used help in establishing the type of fouling
The next basic information, which is missing in your case is the type of fouling. Let us discuss the most common type of fouling in sea water, so that we may try to pin point the fouling in your case
- Crystallization Fouling.
This type of fouling occur when deposition of calcium carbonate, calcium sulphate and other salts occur due to increase in temperature as these salts have a solubility in water which diminishes with increasing temperature. Thus leading to crystallization of deposits of the salts on the heat exchanger tubes and reducing its performance
- Corrosion fouling:
Although this type of fouling is rare in lube oil cooler, but it does not means that it would not occur for lube oil coolers. In this case some metals are oxidized to produce insulating layers of oxides on the tubes
- Biological fouling
In sea water Service exchanger the most common type is Biological Fouling. In this case a whole range of biological growths form on heat exchanger tubes in seawater. The species attached range from micro-organisms (bacteria, algae) to macro organisms (mussels, barnacles, etc
Proper identification of biological range is necessary for the selection of biocide
- Particulate fouling.
Sea water may contain many types of silt, mud, sand or other finely divided particles that may settle on the heat exchanger surfaces and act as an insulating layer. This type of Fouling is called particulate fouling
You should establish what type of fouling is occurring in your case as this is deemed mandatory to suggest remedy
Fouling may be predominant in sea water system due to following factors<ul>
- Surface temperature
The temperature at the interface between the seawater and the solid surface is of crucial importance. For crystalline fouling, the deposition is small at temperatures below 60oC but can become serious at elevated temperatures
Please do check the out let temperature of your exchanger. This might be one of the cause of rapid fouling. I have seen crystallization fouling over a period of a month for steam condensers with outlet temperature operating with water outlet temperature of 65 Deg C
Please see attached file for impact of temperature on different type of fouling
- Bulk temperature:
It may be noted that Biological growth becomes faster as bulk temperature increases from ambient values. At high bulk temperatures the organisms may be killed; however, long residence times may be required at elevated bulk temperatures, to kill the organisms present
- Water velocity:
Water velocity generally has only a small effect on crystalline fouling at lower velocities but may tend to shear off the crystalline deposits at higher velocities.
Biological fouling rate tend to increase with velocity at low velocities, reflecting the need to supply nutrients to the surface which needs at least a low flow rate to sustain mass transfer. However, the risk tend to reduce at high velocities. This is the main reason that water treatment supplier recommends using water velocities in the range of 1.5-2.0 m/sec
Please check water velocities as in most cases I have seen the problem occur due to low velocities through exchanger and due to use of high over design factor at design phase
- Solids.
In seawater, sand is the most prevalent solid and erosion may be expected for sand particles with sizes greater that around 50 micrometres at concentrations no more than a few hundred ppm.
It is pertinent to mention that Titanium and Superduplex alloys are much less prone to erosion-corrosion than copper-based alloys.
I am not going into the details of most suitable material for sea water service for your application as the material you have indicated is used on many applications
Coming back to the remedy please do consult a water treatment company for suggestion of proper biocide or shock polymeric dozing at the inlet of exchanger to avoid frequent cleaning
You may consult http://www.merusonline.com/theproduct for supply of merus rings which may be effectively used for your specific case. I my self donot have any experience of using such rings, however, I have heard good experience for using in different type of fouling
Regarding chemical cleaning, it may be noted that without knowing the type of scale you can not choose an anti scalant and a corrosion inhibitor. However, you may find good guide lines in ASM book Corrosion in Petrochemical Industries
To my best of knowledge sulfamic acid is not a very good chemical cleaning agent . Instead 2-10 % HCl may be tried with a good corrosion inhibitor. We have used even 10 % HCL inhabited at 60-65 Deg C for 4 hours for CaCO3 deposits
You may find a number of corrosion inhibitors for cooper and alloys from following companies
- Armohib ( http://sc.akzonobel....rmohibfinal.pdf)
- IBIT (http://www.asahi-che...t/cleaning.html)
- Rodine (http://www.henkelna....odine-18842.htm)
Please do test the effectiveness of the inhibitor before implementing in the filed
Hope the information will help