Hello friends,
I am a mechanical engineer working for a tank-farm project located in a CCGT project, in Turkey.
Venting of the storage tanks is a task that I came across unplanned. I took over this task after realizing that the designer did nothing but "copied without questioning" the vent design that came with original specifications provided by the customer.
So lately I was all over the internet and API 650 & 2000 to determine the required venting for our tanks.
Our tanks are water tanks, cargo varying from demineralized water to running water.
Below summarizes the reasoning I conducted:
Since the tanks store water, I considered only the normal venting case since the tank cargos are unflammable (I MAY BE WRONG).
The tanks are built as per API 650, so I took the MAWP and MAWV as the roof weight and 1 inch of water (249 Pa), respectively.
To calculate the required inbreathing and outbreathing flowrates, I added the values obtained from Table 1 and Table 2 of API 2000 (1998 issue). I picked the data from Tables as per the boiling point of water, however, Im doubtful about this, since API 2000 is targeted on petroleum products.
To obtain the required vent area, I used the formula given at Clause 4.6.1.2, applying the Coefficient of Discharge, K, as well.
The calculation sequence is roughly the same as in
13_Venting_requirements.pdf 19.18KB
390 downloads which I got from http://www.eng-tips.....cfm?qid=311070. I copied the sequence in this spreadsheet except for the MAWV value, which I took as 1 inch of water.
So, I have these questions to ask to verify myself,
1. Does the fact that the stored products being water make any difference for the vent size requirement ? If so, in which direction ?
2. Is "inch of water" a safe assumption for MAWV ? Is there any way to determine it ?
3. All these calculations are valid for simple open vent areas. And our vent nozzles are equipped with goose necks, CO2 absorbers or pressure-vacuum relief valves. Should I insert this factor to the calculation, if so, how to determine the factor ? Would it have a significant effect over the estimated pressure difference ?
4. Should I also consider the emergency venting requirement ?
I really need your help because we have limited time to make extra venting modifications, and since it is a matter of safety.
Kind regards,
Umut