Not sure if this has been finalised yet but I thought I would add some information.
Anshul from what you have mentioned so far you should be able to size your sub-header(s) to the main header.
Firstly, we need to understand what are the tie-in back pressure for both the LP and HP system.
Firstly, at said 4 barg back-pressure is there a relieving scenario occurring from any of your relieving points (i.e. PSV's, BDV's, etc.)?
If yes, then you will not be able to use conventional PSVs (should the PSV set pressures be 10 barg & 14.8 barg) as the back pressure will be 4 barg plus the addition of any pressure drop within the sub-header and the PSV tailpipe. Hence greater than 4 barg and therefore higher than the 10% allowable back pressure guideline (API 521 Section 7.3.1.3.1) for conventional PSVs. As such you will need to use Balanced type PSVs which allow 30-50% back pressure (will vary depending on the specific vendor).
The sizing of the flare header is not solely dependent on the relieving sources but you must size the header such that the following are taken into consideration:
1. Back pressure at the relieving source is such that the PSV will not be affected. i.e. back pressure is not higher than 10% of the set pressure for Conventional PSVs and is not higher than 30-50% for Balanced PSVs.
2. Mach No. within the header and tail pipe. Consider a Mach No. limit of 0.5-0.6 for headers and up to 0.7-0.8 for tailpipes. This will depend of the Clients requirements but these are some standard guidelines to go with.
3. Headers should be sized based on REQUIRED flowrates, while tailpipes should be sized based on RATED flowrates.
4. Rho.V2 criteria is important to observe for vibration problems amongst others. I would suggest that anything below 100,000 kg/m/s2 is acceptable without the requirement for AIV studies. Anything above 150,000 kg/m/s2 is probably excessive. Again these figures will depend on the Client requirements, and what theory you read.
Now should your relieving sources not be opening at 4 barg, and no other source is attached to your header then there is no requirement from your side. You need to size your headers for when your PSVs are "popping". If this is not occurring at the case which gives a tie-in back pressure of 4 barg then you must obtain a tie-in pressure at the time that your PSVs are "popping".
Hope this helps and that anything i have mentioned is not incorrect. I'm sure it will be corrected if that is the case.
Matt