With reference Mr. Justin question, generally, in the Petrochemical Industries, most of the equipment will be equipped with standby PSV to release main PSV for overhauling and test purpose. Single PSV installed where the protected equipment got standby one (typically filters, pumps). Hence related equipment can be isolated and depressurized prior to removal of the single PSV irrespective of whether PSV designed for fire/thermal relief purpose.
In Petrochemical Industries, during normal operation time even though most of the PSV (designed for fire service ) does not come into picture however any normal operating condition can become uncontrolled situation in the petrochemical plant where operator cannot relieve the pressure by opening the bypass of PSV to control the pressure in case of fire or ay other operation abnormality. Hence each single PSV needs HAZOP studies by operating personnel and proper procedure needs to be established for maintenance job according to its service. Sometime Single PSV used in different purpose in the petrochemical plant and it can be released without isolating the equipment.
Example, thermal PSV is provided in the propane or ethane liquid pump suction line to protect pump from over pressurization due to thermal expansion when pump kept isolated with liquid. In that case during outage of PSV pump suction & discharge valve will be kept locked opened to protect from over pressurization. Otherwise Pumps isolation valves must be spaded at immediate flange to remove this single PSV which leads to pump outage and additional spading jobs. So it is purely based on operation/ technical department to decide every PSV according to HAZOP studies and guidelines to release the single PSV.
Edited by Babu Prasad, 14 September 2013 - 07:12 PM.