Hi,
In all my previous projects, SDV (shut down valve) is loacted on the Tank liquid outlet line (which is Pump Suction Line). As per my understadning, this SDV loacation is correct. SDV on the Pump suction line will limit & isolate the Tank inventory mainly during Fire. During Fire, we do need to isolate invetory from rotating parts of the pumps. However I got comment from Seniors to shift this SDV on the Pump discharge to isolate total system (Tank & Pump).
According to me, Typical Cause & Effect of Tank-Pump System is as follows :
1. On high - high level, Tank inlet SDV will close
2. On low-low level (or on low-low Pump Suction Pressure) : Pump motor will stop (pump trip)
3. During Fire, Tank oultet SDV will close.
Hence. No additional SDV are required in this tank-pump sys.
Please correct me if I am wrong.
Regards,
Shekhar Dhuri