Thanks Ankur for your Valuable Input and time,
1. My thinking was PALL is required to give alarm and ESD action when ever there is low low pressure in the system which may happen due to pipe rupture, flange leakage or it may be due to some other reason, so that we can separate the system from source and stop further spillage of hydrocarbons.
due of check valve presence between flow lines and headers PALL on flow line will not help to detect low pressure in production header and Test headers.
2. I fully agree with you that flow lines will see the highest pressure during choke valve failure, mean time my thinking was even production header and test header can also see the almost same pressure may be lightly less than flow lines ( because flow lines are of only 15 m length), but because of check valve on flow lines we will not be able to see what is the pressure increase in the headers with the help of PAHH on flow lines. we have PSV set at 70 barg on flow lines which helps to relive the fluid between choke valve and check valve on flow line. my concern was how to relive the fluid between check valve and SDV on production header if Headers are also reaches 70 barg along with flow line before PSV opens.
3. PSV for thermal expansion is not required because of GOR is 25. PSV may be required during choke valve failure or blocked outlet case.
I raised this question to find out what is right method because In 2 of my previous projects ( offshore Plants) we considered check valve as restriction and provided the PAHH,PALL and PSV.
this time I was doing another project for different client and I was referring to their FEED and other platform project that have the system which I showed in the sketch.
We are doing EPC job and if we don't provide PALL, PAHH and PSV it is will be profit us ( and even client is not asking for it ) and I was just trying to find out which one is the right method to protect the system.
Thanks and Regards
Rakesh