I have come across an interesting case.
On one of our facilities, there is a level control valve which takes the water from the prodn sep to the water treatment skid. The Prodn sep operates at 1300 psi, and the water treatment skid operates at 50psi. There is no choke / RO in this line. In other words, all the pressure drop occurs across this valve. The flowrate is quite small as well. (circa anywhere between 2 - 20 bbls / day) The valve internals need to be changed frequently, which is not surprising due to the large DP across the valve.
The valve was originally sized for a much larger flowrate. The existing valve has a CV of 0.35 and when we did a fresh sizing case we determined that the valve may need a much smaller CV of ard 0.002 in its maximum case.
However, when we looked at the process trends, we noticed that the valve position actually stays closed for some time, then swings 100% open…stays open briefly, then closes again to allow level to build in the separator. While this may be fine for some methods of level control, I am not sure if this is the best approach to have a valve opening and closing against such a large pressure drop. It may be better to have the valve operate between a more reasonable range and not fully open / fully close often (or at all.) i.e have the valve between 20% - 80% open.
At the moment, I am not convinced that changing the valve to a smaller oner will fix the problem of having to change internals annualy. According to me, whatever valve is used the method of control (i.e full open / full closed) will not be changed by changing the valve. The onyl difference with a different size valve will be the time the valve stays open / closed.
In summary:
This is a two part problem. On one hand you have a valve that may be too large for current service, and on the other hand the control method may need to be adjusted. We should try to fix / tune the exisitng valve and monitor operation before buying / changing a valve...correct?
My question: How can we ‘tune’ the level control valve to have it operating more in a modular manner rather than this on/off manner? BTW the controller is a PID controller.