normally cooling tower blow down either contineous or intermittent is done from cooling tower bottom. is it not possible to do it from cooling water return header so that blow down pumping to ETP power cost as well as pump Installation cost can be saved.
|

Cooling Tower Blow Down Cost Saving
#1
Posted 20 November 2013 - 09:35 AM
#2
Posted 20 November 2013 - 12:06 PM
k.j.
The location of outgoing blow down is bottom of the cooling tower basin because the concentration of dissolved solids is at the highest value there among the whole loop due to fluid stagnant condition after evaporation in cooling tower...
#3
Posted 21 November 2013 - 02:21 AM
normally cooling tower blow down either contineous or intermittent is done from cooling tower bottom. is it not possible to do it from cooling water return header so that blow down pumping to ETP power cost as well as pump Installation cost can be saved.
You can try doing a lab analysis of the dissolved solids etc. at both locations. A differential will be instructive.
#4
Posted 21 November 2013 - 05:20 AM
Hi ,
What you are describing is the way the Cooling water system I was operating ( 5000 m3/h capacity) was working a couple of years ago !
You should consult vendors and or water treatment company for 2nd opinion .
Breizh
Edited by breizh, 21 November 2013 - 08:25 PM.
#5
Posted 21 November 2013 - 08:35 AM
#6
Posted 22 November 2013 - 02:51 AM
@ thorium Actualy cooling tower blowdown done from basin bottom which goes to blowdown pit and from that with pump it goes to ETP.
I have given basin bottom sample to check how much it is differing from circuilation header.
#7
Posted 23 November 2013 - 08:08 PM
ok basin blowdown and return header analysis is as
parameter basin bottom return header
PH 7.0 7.1
conductivity 1874 1862
turbidity 13 10
TS 1398 1396
TH 829 792
chloride 206 225
silica 128 119
TDS 1358 1354
SS 40 42
As per cooling water treatmnet company treatment chemicals are dosed in supply header so direct blowdown from return header will be loss of that chemicals.
#8
Posted 24 November 2013 - 01:30 AM
K.j .,
As stated earlier your proposal is fine to me, your system is well balanced !
Breizh
Similar Topics
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
![]() What Kind Of Cooling System Should I Use To Cool Down A Jacketed MixinStarted by Guest_HollyBoni_* , 31 Jan 2025 |
|
![]() |
||
Ll Extraction TowerStarted by Guest_dpunnn_* , 22 Nov 2024 |
|
![]() |
||
Effect Of Continuous Blow Down To Boiler Feed WaterStarted by Guest_Dyames027_* , 21 Nov 2024 |
|
![]() |
||
![]() ![]() Energy Saving In Pump By Reducing Pressure Drop In Downstream PipelineStarted by Guest_Srinivas Agastheeswaran_* , 19 Nov 2024 |
|
![]() |