I have a piping system that we want to protect from flame propagation, if the arresting unit is <3 ft away from the inlet to a thermal oxidizer, would a detonation arrester be required or is a flame arrester acceptable? I have called vendors and gotten different responses.
|

Detonation Arrester Vs Flame Arrester
Started by ryn376, Nov 20 2013 03:51 PM
2 replies to this topic
Share this topic:
#1
Posted 20 November 2013 - 03:51 PM
#2
Posted 20 November 2013 - 04:34 PM
Basically, can the flame speed plus (or minus, depending on flow) gas velocity obtain sonic speed before the arrestor? What diameter is the pipe? What is the fuel?
#3
Posted 20 November 2013 - 07:38 PM
I would consult the thermal oxidizer supplier. And, I don't think you can stop a detonation. But you can stop a deflagration.
Bobby