Hi,
When sizing PSV, we account for 10% overpressure for blocked outlet cases and 21% for fire cases. Why are these values set up as such other than they are stated in the code(s)?
Thanks,
Sherif
|
Posted 20 May 2014 - 09:38 AM
Hi,
When sizing PSV, we account for 10% overpressure for blocked outlet cases and 21% for fire cases. Why are these values set up as such other than they are stated in the code(s)?
Thanks,
Sherif
Posted 20 May 2014 - 10:26 AM
Sherif,
Which code(s) and how amount?
Posted 20 May 2014 - 10:36 AM
Fallah,
in ASME, the overpressure for fire case is 21%. Also, it is a common practice to have the 10% and 21%. I am just trying to find out the core reason behind these values
Sherif
Posted 20 May 2014 - 12:25 PM
Sherif,
The allowable overpressure of 10% and 21% more than MAWP of a pressure vessel are code requirements (21% came from 10% overpressure more than 110% i.e. 1.1*110%) and common practices are following the ASME code in this regard. But 10% or 21% itself is the optimum value more than MAWP (might be a little bit more or less) prevents the pressure relieving devices to be larger than normal size also allows the maximum operating pressure of the pressure vessel to be close enough to its design pressure.
Edited by fallah, 20 May 2014 - 12:33 PM.
Posted 21 May 2014 - 05:59 AM
I believe the 110% is the 10% more than the MAWP. Right?
Why adding another 10% though?
Sherif
Posted 21 May 2014 - 07:15 AM
Sherif,
My answers are in red color as follows:
I believe the 110% is the 10% more than the MAWP. Right?
Actually, in general 110% is 10% more than PSV set pressure. If set pressure would be equal to MAWP, then 110% is 10% more than MAWP as maximum overpressure.
Why adding another 10% though?
For fire case another 10% to be added for lowering the PSV size because in most fire cases it can be supposed the engulfed vessel along with the PSV would be destroyed.
Posted 23 May 2014 - 07:07 AM
Thanks Fallah
![]() Liquid Liquid Separator SizingStarted by Guest_Kentucky08_* , 03 Apr 2025 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |
||
Batch Adsorption: H/d Ratio For Vessel SizingStarted by Guest_Victor_process_Engineer_* , 28 Feb 2025 |
|
![]() |
||
![]() Separator Sizing Step By Step ProcedureStarted by Guest_krishnamurthy_* , 06 Apr 2023 |
|
![]() |
||
Petrosim Tray SizingStarted by Guest_tomr91_* , 27 Feb 2025 |
|
![]() |