Sdv Fail Position
sdv fail position security
#1 Ariel
Ariel
  • 49 posts
Posted 23 July 2015 - 01:28 PM
Hello!
I need to share a personal opinion about SDV fail position.
Many times, I read or hear something like that:
A shutdown valve actuator shall pneumatic/hydraulic fail-safe spring-return type. Generally a shutdown valve failed to close (FC).”
I guess this comes from the possibility that you could have a problem with your instrument gas supply.
But….in cases where I have a completely reliable system to generate instrument gas (in this case air), provided by:
·         Two twin compressors (one is back up).
·         10m3 recipient for 24 hours consume.
·         Pressure transmitter to indicate and alarm of low-pressure air.
·         Independent pressure transmitter to generate emergency shut down in case of low low-pressure air (usually 4 bar).
Can I choose to install doble- action actuator? Especially for big ASME #600 valves (> 12in)?.
Thera are:
·         Less expensive
·         Much more smaller
·         Less maintenance need
·         Easy re-open or operate in start up/shut down operation. An operator can open/close de valve from a control panel beside the valve.
In advance, thanks for your expert opinions!
Ariel
#2 Bobby Strain
Posted 23 July 2015 - 01:50 PM
If it is a shutdown valve, it should fail closed. Unless, maybe, you commit to a program to ensure that it is as reliable as it needs to be. But that would be a hard sell. Especially to your insurance provider.
#3 fallah
  • 5,019 posts
Posted 24 July 2015 - 01:06 AM
Ariel,
As far as i know in SDV's, type of actuators don't relate to their fail safe position; they should be fail closed with every type of actuator...
#4 Ariel
Ariel
  • 49 posts
Posted 24 July 2015 - 05:50 AM
Ariel,
fallah, thanks for your answer.
Yes of course I agree with you and SDV must be fail closed. What I wanted to ask, maybe I did it in a wrong way, if it´s safe enough to use a double acting actuator to close a SDV valve.
Always consider the reliable air instrument system that I just have described.
Thanks in advance.
Ariel
Edited by Ariel, 24 July 2015 - 05:51 AM.
#5 Ariel
Ariel
  • 49 posts
Posted 24 July 2015 - 08:19 AM
Bobby thanks for you answer.
In this case, we performed a HAZOP study to analyze de safety of the system.  I think this could be a kind of backrest for a double effect actuator selection based on air system reliability.
Definitively I did my question badly because you are the second person that misunderstanding the main topic.  I want to emphasize that the SDV valve has been mounted with a double effect actuator and not with a simple spring return actuator like is common. Do you think it´s an unsafe situation?
Thanks again.
Ariel