Does anyone have experience using "off-the-shelf" steam flash separator devices designed and provided by vendors (e.g. Spirax Sarco) for large flows in a condensate recovery system? I have in mind flows like 50,000 lb/hr of 160 psi condensate. Spirax Sarco has Flash Vessel Sizing Chart (see Fig 14.6.4 http://www.spiraxsar...esources/Pages/Steam-Engineering-Tutorials/condensate-recovery/flash-steam.aspx ) which indicates they have predesigned equipment to handle large condensate flows.
|

Steam Flash Separator Device In Condensate Recovery System
#1
Posted 03 September 2015 - 01:31 PM
#2
Posted 03 September 2015 - 02:53 PM
Your link requires a password. Have you checked the sizing with your favorite software? This shouldn't be rocket science.
Bobby
#4
Posted 04 September 2015 - 05:29 AM
#5
Posted 04 September 2015 - 05:30 AM
Does anyone have experience using "off-the-shelf" steam flash separator devices designed and provided by vendors (e.g. Spirax Sarco) for large flows in a condensate recovery system?No, I don't, but as Bobby already said: this is not rocket science.
It is very simple to size such a separator and see whether the Spirax Sarco size makes sense.
What is the flash steam pressure (pressure in separator at which the condensate is to be flashed)?
What is the flash steam to be used for?
#6
Posted 05 September 2015 - 12:10 AM
http://www.sugartech...essel/index.php
http://www.pennseparator.com/fssel.htm
Hi,
Consider the resources attached to support your work.
Breizh
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
![]() Liquid Liquid Separator SizingStarted by Guest_Kentucky08_* , 03 Apr 2025 |
|
![]() |
||
Converting Superheated Steam To Saturated SteamStarted by Guest_addiesalsabil_* , 10 Sep 2023 |
|
![]() |