Does any one have experience with relief valve in cryogenic vessel? This is the problem we are struggling with.
We have a vacuum jacketed liquid hydrogen storage vessel with a stamped MAWP of 77 psig with full vaccum. The vessel is limited by the thickness of the head with 92 psig design pressure (77 psig + 14.7 for vacuum) per UG-32 equation (1). Liquid is transferred out of the vessel by the use of a closed loop pressure build coil (vaporizer).
The relief devices for this vessel is a 4" x 6" spring actuated relief valve and an 8" rupture disc. Our calculations have shown that the relief valve capacity is more than sufficient to accommodate a complete failure of the pressure build coil (i.e. the vaporizer output at maximum capacity).
Per ASME Section VIII, the relief valve is set to the vessel MAWP. What should be the set burst pressure of the rupture disc? The rupture disc capacity was size to accommodate a complete failure of the vacuum system (i.e. unexpected source of external heat). Can the burst pressure be set to 92 psig without violating UG-134(

Have I included the necessary info above?