Thermal Expansion Relief Valve In Lng Service
lng trv
#1 nivedita
nivedita
  • 3 posts
Posted 04 April 2016 - 08:44 AM
i have 2 trv in series for a line cooing from liquifaction ino the LNG storagae tank.
The line design pressure is 150psig. Athough it is a 2 phase line which i was worried about ,on the P&ID it is split into vapor and liquid lines.
so the line size is 2" and the following are the conds -
for 2 phase line
Press-  29 psia
temp-  -243.6F
Comp-95%methane
1.44 % co2
95% methane
0.03% oxygen
vapor frac 0.0530
the line splits to liquid and vapor lines
both lines have 150 psig design pressure
I have got a this calc for liquid line as per API
SET PRESSURE 150 psig OVERPRESSURE 10%         HEAT SOURCE solar radiation MAXIMUM HEAT EXCHANGER DUTY 3.30E+02 Btu/hr/ft2 DIAMETER OF PIPE 2 IN LENGTH OF PIPE 20 FT (assumed) SURFACE AREA OF PIPE 20.944 FT2 φ FOR SOLAR RADIATION (330 Btu/h-ft2 applied to surface area)           SPECIFIC GRAVITY, d 0.43   CUBIC EXPANSION COEFFICIENT, αv 0.0009 1/°F MAXIMUM HEAT TRANSFER RATE, φ 1100.00 btu/hr SPECIFIC HEAT, c 1.115 Btu/lb F             RELEIF RATE 0.004168 gpm VISCOSITY 1.066 cP
For gas phase i have used this calc
Q     Length of pipe 10 assume Volume of the pipe 10.5 FT3       Pressure Max pressure of pipe 150 Psig         0.179 scfm   10.760
scfh
Q= ((V)*(MAEP/14.7)*(520/T1 - 520/T2))/60
Based on the following assumption
T1 = Degrees R, with 50 OF T2 = Degrees R, with 100 OF   Based on worst case temperature rise from ambient heat gain based on 50 degree F rise in one hour
Please help me calculate the gas flow rate for the TRV i know it is 3/4"x1"
but my boss needs to know
#2 nivedita
nivedita
  • 3 posts
Posted 04 April 2016 - 09:34 AM
sorry it is a pipe so solar radiation is 330Btu/hr ft2 F
Also i sent the two phase stream through a separator hence I got my vapor and liquid conds
#3 ankur2061
ankur2061
  • Forum Moderator
  • 2,484 posts
Posted 04 April 2016 - 11:58 AM
Nivedita,
Please have a look at the link provided below:
http://www.cheresour...e-relief-valve/
#4 Art Montemayor
Posted 04 April 2016 - 12:51 PM
nivedita:
Our members' responses are all valuable information to add to your experience and knowledge bank.  However, there are some very basic and important notes I want to add to this thread because I detect a misunderstanding on your part of what, basically, constitutes the purpose and the use of a Thermal Relief Valve (TRV).
First, please make note that the very title, "Thermal Relief Valve", is actually a misnomer employed solely due to custom and not an accurate title.  This valve DOES NOT RELIEVE TEMPERATURE(S).  It is designed to relieve the normal hydraulic pressure exerted by a blocked-in LIQUID FLUID when subjected to unexpected external heat input(s) such as ambient or solar heating.  Normally, the fluid in question is supercooled liquid and its designed relief flow rate is very, very small - since the design basis only involves hydraulic pressure caused by liquid expansion due to temperature increase.
This is specifically pointed out by our member Erwin Apriandi and unfortunately is not specifically mentioned by our Ankur Srivastava in the referenced thread - although he does identify the fact that the TRV is not used in 2-phase environments.  The obvious reason for it not being applicable in 2-phase environments is that the valve is not meant to relieve vapors or gases.  Additionally, since the designed relief flow is very small (since a small hydraulic liquid expansion causes large pressure increases - due to the liquid's relative incompressibility) the corresponding TRV size is normally very small also (usually ½ to ¾ inch diameter).
I make mention of the above design basis for a TRV because I believe that basic data for your application does not seem to indicate an application for such a relief valve.  You may be misunderstanding the design and application of this relief valve.  It may be that I don't understand your application.  I fail to understand the use of 2 TRVs in "series" - and certainly in 2-phase service.
Perhaps a detailed sketch of what you propose would better explain your proposal.
P.S. - Your thread title, "Thermal Expansion Of Relief Valve", doesn't make sense.  The TRV is not thermally expanding; it is the fluid.  I am changing the title to reflect what I think you mean to state.
#5 S.AHMAD
S.AHMAD
  • 786 posts
Posted 22 April 2016 - 11:32 PM
Nivedita,
I believe that what you mean is TRV in parallel that is two TRVs are installed on the same pipe where blocked-in situation may occur. Normally 1 TRV is sufficient.
However, probably what you mean is a piggy back installation.This is what I strongly believe. A good reason for this type of installation is to save piping cost.
Simplified PFD may project a more clearer picture.
Edited by S.AHMAD, 22 April 2016 - 11:58 PM.
#6 nivedita12
nivedita12
  • 46 posts
Posted 25 May 2016 - 12:14 PM
Thank you all for the valuable input got it and fixed my valve calculations