Hydrotest Pressure For Pipeline
#1
Posted 30 May 2016 - 10:34 AM
#2
Posted 30 May 2016 - 01:49 PM
farid.k,
At first, please specify the design code of the piping system you described...
#3
Posted 30 May 2016 - 05:52 PM
Edited by farid.k, 30 May 2016 - 05:54 PM.
#4
Posted 30 May 2016 - 07:43 PM
stated at last page of pipe spec, it mention ANSI B31-3B 1991
#5
Posted 31 May 2016 - 01:32 AM
stated at last page of pipe spec, it mention ANSI B31-3B 1991
farid.k,
As long as the hydro-test pressure equal to 1.5 times the piping design pressure will produce a stress not to be exceeded than the relevant yield strength at test temperature, there would be no concern about the hydro-test pressure being above design pressure...
#6
Posted 31 May 2016 - 02:49 AM
#7
Posted 31 May 2016 - 03:11 AM
Sorry as I don't really know where to get yield strength at test pressure. Will it be mention in the pipe spec document?
farid.k,
No, but the allowable stress value by which the pipe thickness has been calculated based on selected design pressure had already been specified such that 1.5 times of design pressure won't result in a stress higher than the mentioned specified allowable stress...
#8
Posted 31 May 2016 - 09:20 AM
Farid,
Although I confirm what Mr. Fallah said, most of the time it is not required to exactly consider the hydrotest pressure 1.5 times the design pressure.
In many case, you can practically test the line with pressure 1.3 times the design. So, if you are sure about not allowing to run above 50 barg, you may hydrotest the line on 50 barg.
Mahdi
#9
Posted 31 May 2016 - 11:42 AM
Farid,
Although I confirm what Mr. Fallah said, most of the time it is not required to exactly consider the hydrotest pressure 1.5 times the design pressure.
In many case, you can practically test the line with pressure 1.3 times the design. So, if you are sure about not allowing to run above 50 barg, you may hydrotest the line on 50 barg.
Mahdi
Thanks Mahdi for the suggestion. Yea, I just simply put test pressure = 48 barg which is 2 barg below the design pressure stated in the pipe spec and 8 barg above my process design pressure. Just that I deviate what has been suggested from ASME standard which 1.5 x design pressure. Is it OK to deviate? And any basis for the 1.3 x design pressure?
#10
Posted 31 May 2016 - 12:01 PM
stated at last page of pipe spec, it mention ANSI B31-3B 1991
If the design code of the piping is ASME/ANSI B31.3, then you are not allowed to do the hydrotest pressure below 1.5 times of the piping design pressure. Indeed, hydrotest pressure with 1.3 times of design pressure is relevant to pressure vessels mostly being designed based on AMSE Sec.VIII Div.I.
#11
Posted 31 May 2016 - 01:46 PM
Farid,
You can check the below links:
http://www.wermac.or...re_testing.html
https://pgjonline.co...-determination/
In addition you can search the topic in "Pipeline rules of thumb handbook". By: McAlister
Mahdi
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |
||
Pressure Of An Isolated Flow In PipeStarted by Guest_phoroogh_* , 30 Jan 2025 |
|
![]() |
||
![]() Maximum Allowable Accumulated PressureStarted by Guest_mahmooddalvi09_* , 30 Jan 2025 |
|
![]() |
||
Screw Compressor Suction Pressure DeterminationStarted by Guest_Deicide Dunkelheit_* , 22 Jan 2025 |
|
![]() |