Control Valve Flow Characteristics
7 replies to this topic
#1 shahidulislam48
shahidulislam48
  • 104 posts
Posted 09 May 2017 - 05:47 AM
I had been working with control valve data sheet. It had been provided by me to manufacturer but there was no mention of flow characteristics in the data sheet. When the manufacturer had provided us the data sheet according to their products specifications I had found that there was "Equal Percentage" as flow characteristics.
Is there any criteria or procedure so that we can verify the flow characteristics that is provided by the manufacturer is appropriate according to our process?
Thanks in advance.
Shahidul Islam
#2 latexman
  • 1,809 posts
Posted 09 May 2017 - 07:25 AM
Valve manufacturers always provide the wide open Cv or Kv, and usually provide a table with 5-10 data points of valve % open vs. Cv or Kv.
#3 shahidulislam48
shahidulislam48
  • 104 posts
Posted 10 May 2017 - 01:27 AM
But how could I justify their recommended flow characteristic is suitable for my process?
#4 ankur2061
ankur2061
  • Forum Moderator
  • 2,484 posts
Posted 10 May 2017 - 02:13 AM
Download the excel spreadsheet from my post (#5) in the attached link to know description and application of linear and equal percentage control valves:
https://www.cheresou...gas-and-liquid/
Also refer these other links to understand about linear and equal percentage control valves:
https://www.cheresou...haracteristics/
https://www.cheresou...considerations/
#5 shahidulislam48
shahidulislam48
  • 104 posts
Posted 13 May 2017 - 11:04 PM
Thank you Sir.
#6 breizh
  • 6,715 posts
Posted 14 May 2017 - 01:50 AM
Some training materials you may found of interest to support your work .
Hope this is helping you .
#7 fallah
  • 5,019 posts
Posted 14 May 2017 - 04:49 AM
Shahidul Islam,
Hereunder you can find some guidelines to make decision which type of flow characteristics is appropriate for the specified process conditions:
*Equal Percentage:
Is normally applied for temperature and pressure control loops and where minor portion of the control system's pressure drop is through the control valve
*Linear
Is normally applied for level and flow control services and where the major portion of the control system's pressure drop is through the control valve along with required fairly constant pressure drop across the valve
*Quick Opening
Is normally applied for frequent on/off services e.g. for batch processes or where an instantly large flow is required such as deluge systems
#8 shahidulislam48
shahidulislam48
  • 104 posts
Posted 17 May 2017 - 06:15 AM
Thanks Sir fallah and breizh for your support.