Stack Temperature
#1
Posted 24 September 2006 - 02:17 AM
Can anyone explain that "Why Temperature of Stack is kept so high??"
I am working as Assistant Process Engineer in Ammonia unit of a Urea manufacturing plant. There we have a stack of Primary Reformer where we control its temperature at above 340 F. I've not found any reason that why it cannot be lower??
Thank you
#2
Posted 24 September 2006 - 03:28 AM
So probably your Primary Reformer uses a fuel with a high sulfur content...
#3
Posted 24 September 2006 - 04:33 AM
If acid condensation is the main concern at your plant, there is a standard procedure for flue gas dew point estimation, if sulfur content and C/H ratio of your fuels are known.
Please reffer to the following article:
[attachment=300:attachment]
Also, simple "Google" search for terms "Flue gas dew point" or "Cold-end corrosion" will bring you many interesting results.
#4
Posted 24 September 2006 - 10:50 AM
So probably your Primary Reformer uses a fuel with a high sulfur content...
Thanx for reply Gvdlan,
We use natural gas as fuel for Primary Reformer which contains about 10 ppm of total sulphur but the design basis is 300 ppm of total sulphur. Actually, initially sulphur contents in 1980s were high but now it is always below 15 ppm.
Can we cool these flue gases down to 250 F safely??
Do you have any relationship between sulphur contents in fuel gas and stack temperature??
#5
Posted 24 September 2006 - 11:13 AM
http://www.hrsgdesign.com/design0.htm
Go to Process link on the top left side of the page. Click on Acid Dew Point of Flue Gas menu and follow the instructions.
Many of these diagrams are available at engineering handbooks.
#6
Posted 24 September 2006 - 08:43 PM
I would like to add that with a higher exit gas temperature, free gas lift is provided reducing the power requirements for moving/pushing the exhaust gas to the atmosphere.
Thanks,
Gordan
#7
Posted 25 September 2006 - 07:39 AM
I would like to add that with a higher exit gas temperature, free gas lift is provided reducing the power requirements for moving/pushing the exhaust gas to the atmosphere.
Thanks,
Gordan
I think with the higher exit gas temperature, heat losses will increase more quickly as compared to reduction in Power requirement for moving/pushing the exhaust gas to the atmosphere.
Thanx Gordan,
I think gvdlans is right.
#8
Posted 25 September 2006 - 10:06 AM
There has to be an optimum exit gas temperature in order to provide sufficient exhaust gas free lift and not to increase significantly any heat losses while maintining the exhaust gas temperature high enough preventing anu undesired condesation and corrosion.
For the purpose of good engineering discussions, Engineering Software web site -- http://www.engineering-4e.com -- provides an MS Excel file dealing with combustion of coal and oil. For the case of complete combustion, this spreadsheet allows one to calculate and predict the gas composition and find out how low the exhaust temperature can be, with some additional quick steam table look ups and calculations, having no condensation take place.
Since we are dealing with multiple engineering issues, an optimum working point needs to be found for viable and safe operation of the technical equipment.
Thanks,
Gordan
Below are a few plots related to combustion -- complete combustion of coal, oil and gas with air at standard conditions (298 [K] and 1 [atm]) with no heat loss and stoichiometric conditions.








#9
Posted 06 October 2006 - 05:23 AM
i am a chemical engineer from mumbai having a four year experience in methanol plant. you may ask more queries to me regarding primary reformer and the entire methanol plant.
regards.
#10
Posted 08 October 2006 - 08:19 AM
Thanx for sending this spreadsheet. I'll check this out very soon and also I'll apply it to our case.
Best Regards
Attiq
Hello Dhirajkumar,
nice to see u here. I've a number of un-awnsered questions regarding primary reformer as well as secondary reformer. As Soon as I'll find some time, I'll put them on web.
Best Regards,
Attiq
#11
Posted 08 October 2006 - 09:04 AM
I am glad to be of some help.
Thanks,
Gordan
#12
Posted 25 November 2008 - 03:51 AM
#13
Posted 25 November 2008 - 03:48 PM
I do not want to offend anybody but my understanding about how a SMR works is a little different. Everybody is concerned about acid corrosion caused by Sulphur. I do not consider this concern founded.
From what I know, a reformer uses a combined fuel, about 1/3 fresh fuel, and about 2/3 tail gas from the hydrogen separation, I assume it's a PSA. Is that your configuration Attiq?
Now, the source of the tail gas is exactly the SMR feed, and as I know that has very stringent sulphur requirements. Any sulphur in the feed will poison the catalyst; usually people are removing very deep the sulphur before entering the reformer. You should have a feed desulphurization upstream of your SMR. The consequence is that 2/3 of the fuel used is virtually sulphur free.
Now, there is some sulphur, very low (10 ppm as you say) coming with the fresh fuel, and diluted with the tail gas, and generously diluted with combustion air. What would be the stack sulphur content? I can tell you: extremely low.
I think the reason for keeping a certain stack temperature resides in the thermal configuration of the reformer. There are some steam coils there, certain temperature approach maybe have to be kept.
Do not judge the reformer as a normal fire heater, because it is not. Look elsewhere; sulphur is not the culprit this time.
Regards
#14
Posted 11 December 2008 - 06:57 AM
Generally Fuel is not 2/3 tail gas & 1/3 fresh. Its normally 95% fresh & only 5% tail gas,
bcoz in most of the cases a PGR purge gas recovery unit is installed for the production of
additional ammonia.
Also Now a days materials are available where U can reduce flue gas temp to a level
~90 Deg C for maximizing heat recovery. You can go thru an article on my blog related to this.
Here is the link - Improve your Boiler Efficiency
#15
Posted 11 December 2008 - 09:19 AM
I do not want to engage in a dispute, the article is right, you may be right. My understanding was different, I was thinking that we are discussing about a Methane fired furnace, as the original poster confirmed, and not a Coal fired one.
#16
Posted 11 December 2008 - 10:28 PM
I don't think that a healthy discussion is a dispute....
U r right that my article is for boilers where generally coal is fired. However it is applicable to Methane or NG fired furnace also. You will be surprised to note that even in my plant in steam reformer furnace which was NG fired we reduced the temperature to ~100 DegC using a duplex MOC for tubes bcoz of low concentration of Sulphur & its running for last 7 years.
Actually, generally people keep too much margin on temp to be on safer side due to
high uncertainity on exact level of sulphur which is in ppm level. Also, some quality variation may lead to higher Dew Point occassionally. This is the reason of high stack temp in most of the cases.
Similar Topics
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |
||
Cross Over Temperature In Countercurrent Heat ExchangerStarted by Guest_panoska_* , 18 Feb 2025 |
|
![]() |
||
Flowing Temperature- PsvStarted by Guest_stu_* , 17 Feb 2025 |
|
![]() |
||
![]() High Stack Temperature In Ccr HeatersStarted by Guest_viba0124_* , 30 Nov 2024 |
|
![]() |
||
![]() Temperature PredictionStarted by Guest_paul_ohoir_* , 10 Jan 2025 |
|
![]() |