Ethyl Mercaptan Dosing Rate Calculation
lpg ethyl mercaptan odorant
#1 chemilocha
chemilocha
  • 5 posts
Posted 16 October 2019 - 08:28 AM
Guys we are going to operate LPG offloading terminal. I need some reference/sample odorant dosing calculation.
Total LPG flow rate is 224 m3/hr (7 pump working , each pump- 32 m3/hr)
now, i would like to calculate the ethyl mercaptan dosing rate to the LPG flow line @ 15 PPM
can anybody provide me sample calculations or any reference code or standards followed in the oil and gas industry.
Thanks.
#2 Bobby Strain
Posted 16 October 2019 - 09:17 AM
It's simple arithmetic.
#3 breizh
  • 6,790 posts
Posted 16 October 2019 - 06:17 PM
Should be easy if you define PPM volume or PPM mass !
 volume or (mass mercaptan) / volume or (mass LPG) = 15 e-06
mass = volume *density
hope this is helping you
#4 N243
N243
  • 7 posts
Posted 17 October 2019 - 04:25 AM   Best Answer
Hi Chemilocha,
It is indeed simple arithmetic. I can demonstrate below :
Assumptions:
1. Operating flowrate of LPG is taken as 224 m³/hr
2. PPM is expressed in volumetric basis.
Calculation :
  • 15 PPM of Ethyl Mercaptan is the same as 15 mg of Ethyl Mercaptan/ 1 Liter of LPG.
  • Now, LPG flowrate of 224 m³/hr equates to 224000 liters/hr.
  • Multiplying 224,000 Liters/Hour with 15 mg/ liter = 3,360,000 mg of Ethyl Mercaptan required per hour.
  • Answer = 3.36 kg/hr of Ethyl Mercaptan required
I hope this clears up any confusion.
Kind Regards,
N243
#5 breizh
  • 6,790 posts
Posted 17 October 2019 - 05:15 AM
N243,
Very confusing your calculation !  Either it's PPM volume or PPM mass .
note : 1 PPM volume = 1ml ethyl mercaptan per m3 LPG
if PPM volume , the answer is 3.36 liters /hour of Ethyl mercaptan for 224 m3/h of LPG
Edited by breizh, 17 October 2019 - 05:27 AM.
#6 chemilocha
chemilocha
  • 5 posts
Posted 18 October 2019 - 10:05 AM
thanks for your valuable response to the query.
Mr Bobby , yeah its simple arithmetic calculations but i want to verify my calculations with forum members.
Mr breizh , appreciate your answer. its matching with my calculations  too , 3.36 Litres/hour .  :thumbsup:
Now Suppose, if i want to calculate in terms of mass PPM, Considering LPG  density - 530 kg/m3
then  the required ethyl mercaptan at 15 PPM  will be 1.7808 kg/hr ?? :unsure:
regards,
chemilocha
#7 breizh
  • 6,790 posts
Posted 18 October 2019 - 10:33 AM
Yes 1.7808 kg/h . Considering a density of 860 kg/m3 for E.M the flow rate should be about 2.07 l/h .