One of our desuperheater has an steam trap located at distance of 1m downstream from it.
Is it a proper piping design
Edited by muthukmaar, 27 April 2020 - 09:34 PM.
|
Posted 27 April 2020 - 09:32 PM
Edited by muthukmaar, 27 April 2020 - 09:34 PM.
Posted 29 April 2020 - 01:12 AM
Hi,
On steam distribution piping, steam traps should always be installed at least every 30 to 50 meters (can vary based on the company/project philosophy).
Special care must also be taken to install steam traps in locations where there is a chance of liquid pocketing i.e. low points or valves that close for long duration or for that matter if there is vertical lift of the piping.
Check what is applicable in your case.
Regards
Posted 29 April 2020 - 08:46 AM
I think the OP is worried that a steam trap 1 m downstream of a desuperheater may be too close, such that the water droplets and superheated steam may not have come to equilibrium yet. It is a valid concern. Good catch, muthukmaar. I'd advise searching the web for design guidelines on desuperheaters. There are some big names in this business, like Spirax Sarco. My gut is telling me 1 m may be too close. It feels better with 5 m. 30-50 m would be great, as long as there are no take-offs in the 30-50 m span. You also have to be careful about what is downstream of the desuperheater. A turbine? You don't want any droplets in the steam to that!
Posted 29 April 2020 - 09:35 AM
Hi,
You may find good info using this link or you may drop them a email .
https://www.spiraxsa...arn-about-steam
Good luck
Breizh
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
Converting Superheated Steam To Saturated SteamStarted by Guest_addiesalsabil_* , 10 Sep 2023 |
|
![]() |
||
Steam BlowingStarted by Guest_the_avinche2309_* , 24 Feb 2025 |
|
![]() |