Increasing Velocity In Shell Side Of Heat Exchanger
#1
Posted 16 September 2020 - 09:21 PM
I am rating one of the heat exchanger with following configuration
Shell side - cooling water
Tube side - HC gas is cooled.
Shell id and length is all fixed, it is single segmental baffle type exchanger. Existing shell velocity is very less i.e 0.065 m/s.
I dont want to change shell id, but i can change baffle cut / arrangement.
My query is that i want to increase shell side velocity what are the options .
I am using HTRI for rating the exchnager.
Any idea on this shall be useful.
#3
Posted 16 September 2020 - 10:31 PM
Hi,
Agree with Bobby !
Cooling water in a shell , with low velocity means Fouling .
I've attached a document for your consideration .
engineering tips underneath :
http://www.gulleyass...eeringtips.html
Good luck
Breizh
Edited by breizh, 16 September 2020 - 10:59 PM.
#4
Posted 16 September 2020 - 11:24 PM
Exchanger is in service since long and also hc gas is having impurities, so must have been allocated in tubes.
Thanks for path, yes now we are planning to change CW to tube and HC to shell ...
But my major concern is what are the options to increase CW velocity...
Thanks
#5
Posted 17 September 2020 - 03:41 AM
Thanks bobby/breizh.
Exchanger is in service since long and also hc gas is having impurities, so must have been allocated in tubes.
Thanks for path, yes now we are planning to change CW to tube and HC to shell ...
But my major concern is what are the options to increase CW velocity...
Thanks
Once you change the CW to tube you can increase the velocity by changing the diameter of the tubes (most standard dia. are 3/4" or 1"), but you have to keep an eye on the pressure drop across the exchanger, high velocity will lead to high pressure drop, this might lead less flow of cooling water to the exchanger and in turn fouling.
#13
Posted 18 September 2020 - 05:45 AM
Reduction of tube thickness near baffles is usually due to vibration induced fretting... at 0.065 m/s though, there's something strange.
It's just guesswork at the moment though.
Provide:
Process details (flow, pressure, inlet / outlet temperatures)
Current unit details (TEMA Type, Shell ID, length, number of tubes, OD/WT, pitch / arrangement, baffle count, pass count, material)
Easiest way would be to create the as-built unit in HTRI and upload the TEMA from that.
#14
Posted 18 September 2020 - 07:26 PM
@ latexman : existing metallurgy is Carbon steel for shell / Tube / baffles .
@ IGC: i have developed As-built HTRI model also will current configuratoin - but no vibration warnings are there(TEMA-BEM).
Now main concern is how can CW velociiy be increased. Because, we think due to lower velocity there could be concern.
I tried changing CW to tube instead of shell. but no major benefits.
Thanks.
#16
Posted 19 September 2020 - 04:41 AM
@CSNK
I think you are facing two different issues 1) failure of tubes. However, it is not clear what sort of failure you are experiencing 2) reduction of tube thickness particularly near baffles. But could you explain, what makes you think that increasing the cooling water velocity would solve the issue? Reduction in thickness indicates a localised corrosion issue which is less likely to occur on outside tube surface as the service is cooling water. Do you experience reduction in thickness at every baffle and for all tubes ? I think, you should engage with metallurgy engineer on this.
Nevertheless, what general way of understanding the heat exchanger issue is. Input your actual operating parameters and exact (as built) geometry in the HTRI and run it on rating mode. Analyse thermal design output and vibration analysis generated by HTRI. This will flag the concerned area. But make sure, you input every detail of your geometry in HTRI e.g. number of sealing strips, baffle spacing, baffle cut, etc. which i think you can get from exchanger fabrication and GA drawing only. if there is a really vibrational issue, you should see it in HTRI vibration analysis report.
Now, addressing your question of cooling water velocity, since the exchanger is already built and you dont want to change any geomatry of built exchanger then the only way is increasing the flowrate of cooling water as already indicated by Breizh. Increasing baffle cut or increasing shell side passes by increasing number of baffles will increase the velocity too if you can change the tube bundle construction. If you could have cooling water on tube side, then you could block some tubes to increase the velocity. This is done many a times. But on shell side, unfortunately, you have limited option without changing the geomatry. Additionally, from HTRI run outputs you can check, if your leakage streams (B-stream, E-stream, etc) is higher, consider adding sealing strips (only if it warrants any benefit on HTRI run).
Good luck.
Edited by Jiten_process, 19 September 2020 - 04:44 AM.
#17
Posted 12 October 2020 - 07:55 AM
thanks all for reply,
And sorry for delay in reply.
@bobby - we are finally designing new exchanger with CW on tube side and to meet process conditions.
For quick calculation, what is the best way to design a new exchanger and meeting all the norms of TEMA (i.e velocity of CW should be around 1m/s or high, Pressure drop under limit and best design).
Any suggestion / options are welcomed.
#19
Posted 15 October 2020 - 04:17 AM
You have been asked to provide the full process details in order for people to guide you. Any advice that can be given will just be general and will not give the optimal solution.
Personally I'd look at smaller tube ID if I really needed to go up to 10 tube passes or even a different technology like a plate and shell... Again, more info needed.
#20
Posted 20 October 2020 - 08:41 AM
@IGC: On process parameters,
there is HC gas (in shell side - no phase change flow 10 TPH) getting cooled from 82.1 to 40 Deg C.
CW on tube side with inlet temperature of 38 Deg. C (flow and outlet of CW can be varied to meet process constraints).
Main constraints include CW velocity to be more than 1 m/s and shell side Delta P not more than 0.014 kg/cm2.
I have considered tube ID as 19.05 mm with 2.11 mm thickness. Lower than this is not recommended and hence, presently minimum 19.05 mm is selected.
I can achieve all constraints by selecting rod type baffles and increasing number of tube passes.
Hence, wanted opinion / concern on usage of rod baffles and higher of tube passes. Or any other option if possible.
Regards,
#21
Posted 21 October 2020 - 12:52 AM
To get your target water velocity in tubes, you can increase the number of passes.
Bobby
The fluid velocity in water systems should not exceed certain limits to avoid noise and damaging wear and tear of pipes and fitting. The table below can be used as a guide to maxumum veolicities.
Reply to this topic

Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
![]() Recommended Fluid VelocityStarted by Guest_crn_* , 16 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |
||
Cross Over Temperature In Countercurrent Heat ExchangerStarted by Guest_panoska_* , 18 Feb 2025 |
|
![]() |