Can I utilize emergency venting and a fragile roof at the same time?
|


Frangible Roof And Emergency Venting (Storage Tanks Api 650)
#1
Posted 28 July 2022 - 10:57 PM
#2
Posted 29 July 2022 - 02:57 AM
Hi ,
Consider to read the document attached to support your work .
BTW the search engine in this forum is of great support.
EDIT :
https://citeseerx.is...p=rep1&type=pdf
Good luck
Breizh
#3
Posted 29 July 2022 - 11:28 AM
thank you
#4
Posted 29 July 2022 - 12:16 PM
Look in the standards and local fire codes for the tank.
For example, API 650 and U.S. fire codes require either a frangible roof or emergency venting, but not both. However, one may exceed the requirements and provide both. Nothing wrong with that! Especially, if it meets ones relieving strategy.
#5
Posted 30 July 2022 - 01:14 AM
Can I utilize emergency venting and a fragile roof at the same time?
Yes, you can...but it's not needed...