Hi All,
I am designing a fire water pumping system which includes two fire water tanks, one main electric fire pump, one diesel fire pump and 2 jockey pumps (to maintain the pressure in the system). I would like some clarification regarding the fire water start and stop settings to be defined based on NFPA guidelines.
As per NFPA 20, A.14.2.6(4) -

As we are still in design stage, I do not have any final pump curves from vendor to determine the churn pressure (pressure of pump at zero flow). Is it safe to assume an initial guess for the churn pressure based on assumed shutoff pressure calculations as below:
Churn pressure = Differential pressure * 1.25 = 8.6 * 1.25 = 10.75 ~ 10.8 barg
Please confirm the following two points based on my understanding:
1. Based on the above churn pressure assumption, the pump start stop I have calculated are as per below:
Jockey Pump Stop Point = 10.8 + 0.07 = 10.87 barg
Jockey Pump Start Point = 10.87 - 0.68 = 10.19 barg
Main Fire Pump Stop Point = 10.8 + 0.07 = 10.87 barg
Main Fire Pump (electric) Start Point = 10.19 - 0.34 = 9.85 barg
Main Fire Pump (diesel) Start Point = 9.85 - 0.68 = 9.17 barg
Is this understanding correct?
2. If the above fire pump settings are correct, then how does it correlate with the required fire pump discharge pressure of 8.5 barg calculated based on hydraulics?
Your help is highly appreciated! Thanks in advance.