The PCV is a backpressure regulator which functions to keep the entire system at a constant pressure (9 bar) regardless of flow. When the pressure decreases in system to the PSL set point due to opening small drain valve or some leakage, the jockey pump starts to get the system back to 9 bar and then shuts down. I am not sure why the back pressure regulator is required. It may be that there is a demand case for firewater that will require all 3 firewater pumps operating but the overall flow may be such that the pressure would get above 9 bar or even 12 bar, but it may be necessary to run all three pumps at one time to get the flow required, or during testing, but header pressure would then be too high. Thus the PCV was installed to limit the normal operating pressure well below the point where the relief valve relieves but allows the maximum required pressure need by the end users. Sometimes too high a pressure at say a fire hose that someone has to manually hold would create too high flow/velocity an hence too high of a jet reaction force for anyone to be able to hold and control, or there may be other reasons where you don't want to have too high pressure at the end users. In fact it looks like all of the end users are fire hydrant/fire hoses so I think the ability for someone to hold the hose with jet reaction force limits the 9 bar pressure. I would not remove it until I find out what is its function/functions. You may find a description of its function in the Process Design Basis or site Operating Procedure, or other project documentation.
The PSV is the safety relief valve that operates to limit pressure to maximum piping design pressure (12 bar). Typically this is sized for engine overspeed per the appicable NFPA Standard for firewater pumps/systems. This valve must be installed for safety to limit maximum pressue to piping design maximum and cannot be removed. Firewater valves and other inline components are typically designed for a maximum of 175 psig cold working pressure which limits the maximum allowable pressure in the piping, and this corresponds to approximately 12 bar.
Edited by snickster, 14 July 2024 - 10:37 PM.