Hello everyone. I hope you guys are doing fine.
I will start with a little background to let you understand the problem i am having. I am currently working in a glass manufacturing industry.
As the temperatures in summers rises upto 50 Celsius in my country so, I designed a shell and tube exchanger to cool down process air from an Air Blower (maximum pressure of air 0.6 bar). Design was done using HTRI and it successfully lowered air temperature from 78 C to 35 Celsius using chilled water at 22 Celsius. But the problem is during the current climate, with humidity, as soon as air temperature gets lowered than 35 C, moisture condensates and it comes out the outlet where the air is being used. We can stop the water condensing by reducing chilled water flow rate but i am looking for a possible solution to remove moisture (specially when condensed) from the air.
Using Moisture Separator is possible solution but as the air pressure being lower than 1 bar, wouldn't it further bring change into the pressure? the minimum pressure of air that is needed is 0.4 bar. The pipelin of air that is coming out of heat exchanger outlet is 6 inches in diameter. It would be helpful if you can point me in right direction to the possible solution to remove the moisture.
Thanks