Sketch as attached.
For boundary conditions (dynamic specifications):
1. Stream 1 - Pressure (whatever pressure you like)
2. Streams 8 and 10 - Flow (zero so no outflow)
3. Streams 7 and 9 - Pressure (atmospheric maybe, so zero)
Then you need to define the valve characteristics of VLV-100, 101 and 102.
Then you need to define V-100 and 101 details, such as diameter/length/initial liquid level, etc.
Then use event scheduler to set the sequence of valve opening like:
1. All valves are closed prior simulation run
2. When simulation is run, VLV-100 to initially open
3. Then after some time, you open VLV-101
4. Either you set a set time for VLV-101 to open or add a condition in the event scheduler to close VLV-101 when V-100 is full, then you open VLV-102.
5. Close VLV-102 after a set amount of time or when V-101 is full.
This is not exhaustive, but above should nudge you in the right direction.