Hi,
I'm experiencing a case where there are two BDVs installed in a closed volume. The second BDV came into picture while modification of existing plant (addition of new vessel in red color in attached picture). All of the system (green + red) is built and operational. There is an expected change in composition in the process fluid due to which client wants us to check the adequacy of the whole system including the installed BDVs. As marked in attached rough PFD, BDV-2 starts with a time delay of 2 min than BDV-1.
I want to know the strategy how should i proceed with adequacy check for these BDVs.
Strategy 1:
Use all volume (green+red), use existing orifice size of BDV-1 and lets check the time to depressurize. Then open the BDV-2 after 2 min time delay with existing orifice size and check whether this whole system can still depressurize within 15 min. If yes, then both BDVs' orifice are OK. If not, then we need to increase BDV-2 size and fix it to get 15 min depressurization time for the whole system. I don't know if this solution is simulatable or not, but in reality this is what BDVs will be operating actually.
Strategy 2:
Use volume of green part system for BDV-1 adequacy check by fixing the depressurization time of 15 min and calculate the required orifice size. If larger than existing, then inadequate; if smaller or equal to the existing orifice size, then adequate. Same procedure 'separately' for the red part for BDV-2. This procedure i see separates the two volumes which in reality will not be the case.
I hope i'm not missing any technical information to decide about the strategy. Please put up questions in case i missed anything critical.