Posted 06 March 2008 - 04:57 PM
Art,
Thank you for your detailed analysis. I certainly appreciate the time you spent explaining your calculations. After reviewing it, I still have some questions. I also have some clarifications on my system. I hope you have the patience to bear with me on this issue.
My compressor capacity is given in tons of refrigeration. I can multiply by 12,000 Btu/hr/ton and divide by the latent heat of ammonia at condensing conditions and get a capacity in lbs/hr, then convert that to ACFM at suction (storage) conditions. But for the compressor in your example case, your 214 TR does not give me 454 ACFM. Am I missing something here?
I think you have a typo on your line 87 of the Calculation Pad. You calculate 581 lbs/hr vapor from Expansion Valve #1, not #2.
My system has no compressor discharge regulator. I have a rotary screw compressor (and backup) with a slide valve for capacity control.
For your example, I understand the adiabatic flash across the expansion valves and the calculation to determine the quantity of vapor produced. I also understand that the compressor discharge stream is equal to the ammonia vapor created by the heat leak into the tank + the expansion vapor from the two liquid inlet streams. But I’m having difficulty understanding why I have to subtract the vapor created from Expansion Valve #1 and vapor created from the heat leak into the tank system from the total compressor capacity to get the compressor capacity available for unloading.
In your calculation, you take the entire compressor capacity and flow it through the condenser back into the tank to calculate the vapor created by the flash across Expansion Valve #1. If all of the compressor discharge is being recycled back to the tank, what vapor stream is left to unload a railcar? Are you just doing a worst case vapor generation here?
My system has no specific expansion valves. In place of your Expansion Valve #1, I have a level control valve on the outlet of an Ammonia Receiver, which receives liquid ammonia from the condenser on the compressor discharge. When this level control valve opens, the liquid flashes across it, so it acts as an expansion valve. But this level control valve closes when the level in the Ammonia Receiver drops to the set point, so I don’t agree that I have to subtract the vapor created by flashing across this valve from the compressor capacity available for unloading. When there is no unloading going on, heat leak into the tank system creates vapor, which is sent to the compressor suction, all of which is sent to the condenser and receiver, and flashed back into the tank through the level control valve. But when a railcar is unloading into the tank, there may be no ammonia vapor flow through the condenser with liquid flowing back into the tank. Why can’t all of the vapor flow go to the railcar during unloading? I have no back pressure regulator forcing flow through the condenser during unloading, and my level control valve does not stay open.
I also have a question on the heat leak. I can see that the heat leak vapor + the vapor generated from other liquid streams entering the tank cannot exceed the compressor capacity. For my system, in the winter when there is very little heat leak into the system, the compressor can be shut down for extended periods of time with no pressure increase in the tank (no vapor is being generated). Then, to unload a railcar, the compressor must be started, but it is in an unloaded condition, the discharge pressure is much lower than in the summer, and it takes longer to unload a railcar. In fact, we plan to vaporize a small stream of liquid ammonia to feed to the compressor suction for winter unloading – we will be doing the equivalent of creating a heat leak to help with unloading. The vapor from the new heat leak plus the vapor from the unloading liquid flash into the storage tank will be compressed to unload the railcar. In the winter, the railcar may be at only 100 psig, and the vapor generated from Expansion Valve #2 is much less (about 0.051 lbs/lb feed), so we are not running near the compressor capacity. How do you handle your unloading rate calculation in winter conditions?
I have no Expansion Valve #2. In my unloading line, I have manual valves, check valves, and emergency slam valves, but I have no metering or control valve that is equivalent to your Expansion Valve #2. I think I can still do the adiabatic flash calculation for vapor created during unloading (going from railcar conditions to storage conditions), but I can’t define exactly where in the unloading line the flash is occurring. Where the flash is occurring and how to avoid two phase flow in the unloading line was what I was trying to ask in my original post. I'm concerned that if the flow from the railcar flashes in the unloading line, versus right at the tank, it will slow down the unloading rate. Do I need a new expansion valve located at or near the storage tank inlet to maintain liquid phase conditions up to that point and maximize the unloading rate?
Thanks again for all of your help.