From what I’ve read both have suffered classic water hammer damage resulting in ruptured tubes. The tubes that were damaged were on top of the tube bundle with a number of tubes appearing to be crushed. These tubes were not under the steam inlet but about half way down the length of the shell.
Google helped me find quite a bit of information about how to prevent water hammer with nearly all saying that the problem is poor condensate drainage. I only found one reference that attempted to explain what actually is happening in the heat exchanger when it is experiencing water hammer. It was on the Armstrong web site at:
http://www.armstrongpumps.com/Data/ioguide...UBE_I&O.pdf
From this reference:
“In a water heater using steam in the shell, when the demand for hot water ends the steam control valve closes, but there is a good supply of steam left in the shell of the exchanger. As this steam condenses, the pressure drops, often below atmospheric or even practically to full vacuum. This prevents condensate from leaving the shell and sometimes even syphons in condensate from the line beyond the trap. Now, when the steam valve opens again and admits steam to the shell, the rapid condensation, as it strikes the cold condensate, causes streams of water to rise, hitting the top of the shell and bouncing onto the top tubes. Sometimes the breaks in the tubes look as though a 4” spike had been driven through the topside. Other times the tubes may be crushed as if with a blunt chisel over lengths of a few inches or up to two feet.”
We experienced this exact type of damage so I am sure that the problem is water hammer but I am having a problem understanding how this could have happened in our arrangement. The big difference is that the capacity control of our heat exchangers is by varying the condensate flow rather the steam flow, i.e. in our arrangement our heat exchangers were designed to run flooded. There is an automated on/off valve on the steam inlet which is programmed to stay open during the heating season. We should therefore have constant steam pressure on the shell with the condensate level varying with the demand.
A good description of the various ways to control the capacity of steam heat exchangers is in an article found at:
http://www.driedger.ca/ce4_sh/CE4_SH.html
So if the automated on/off steam valve is staying open and we have constant pressure on the shell of the heat exchanger I don’t see how we could experience the rapid condensation that seems to cause the water hammer. I want to check the tuning of the condensate valve but I don’t see how even a big change in the condensate valve position could cause a large swing in steam load or condensation rate. The condensate control valve is 1 ½” (or less?) and the steam inlet is 6” I believe. The load on the glycol side should not change quickly as it is for heating outside air.
I’ve only read about this type of flooded heat exchanger control and have not used it before. I realize that many people will immediately say that you will always have water hammer when your heat exchanger is flooded like ours normally will be but I know that this type of control, although maybe not common, is used and used with success.
So where did we go wrong? Is this type of control prone to water hammer? Can it be avoided? Does this water hammer typically happen when the condensate level is low? Or high? We did not experience water hammer when these two heat exchangers were commissioned but it did happen later.
I can’t seem to come up with an explanation for the water hammering other than maybe, for some reason, the automated on/off valve on the steam inlet is opening and closing when it isn’t supposed to. This valve is programmed to open very slowly over 5 minutes but it is a ball valve so even if it is a crack open there will be a large flow.
Any comments, experience or suggestions would be appreciated.
I have attached a couple of pictures.