DEAR MY FRIEND
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
|

Heat Loss Calculation
Started by WEEWA, Jan 23 2009 01:06 AM
6 replies to this topic
Share this topic:
#1
Posted 23 January 2009 - 01:06 AM
#2
Posted 23 January 2009 - 01:41 AM
QUOTE (WEEWA @ Jan 23 2009, 11:06 AM) <{POST_SNAPBACK}>
DEAR MY FRIEND
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
Dear WEEWA Hello/ Good Morning,
Firstly avoid shouting at everyone else(stop use of Block Capitals)&clarify your background!
General heat transfer formula is Q=UXAXTemperature difference
"Q" is the Heat transfered,
"U" is the Heat transfer Coefficient for particular material invoved,
"A" is area available for(exposed to) heat transfer
"Temperature difference" between Inner(hotter) surface & 'Prevalent ambient(colder) temperatures'
Hope this helps
Qalander
#3
Posted 23 January 2009 - 05:35 AM
QUOTE (Qalander (Chem) @ Jan 23 2009, 02:41 AM) <{POST_SNAPBACK}>
QUOTE (WEEWA @ Jan 23 2009, 11:06 AM) <{POST_SNAPBACK}>
DEAR MY FRIEND
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
Dear WEEWA Hello/ Good Morning,
Firstly avoid shouting at everyone else(stop use of Block Capitals)&clarify your background!
General heat transfer formula is Q=UXAXTemperature difference
"Q" is the Heat transfered,
"U" is the Heat transfer Coefficient for particular material invoved,
"A" is area available for(exposed to) heat transfer
"Temperature difference" between Inner(hotter) surface & 'Prevalent ambient(colder) temperatures'
Hope this helps
Qalander
Dear Qalander,
What you have mentioned is the general equation for heat transfer from heat exchange equipment. The person is asking for heat loss from piping systems, and that is where what you have mentioned does not apply.
Weeva:
Look at the following threads for heat loss from piping systems and equipment which gives equations for calculating heat loss:
http://www.cheresour...amp;qpid=25482#
http://www.cheresour...art=#entry20822
The basic issue in my opinion is whether the exercise is worth doing since in any piping/equipment heating system involving some heat transfer fluid (jacketed piping or equipment), the flanged connections including valves are normally kept uninsulated for the sole purpose of detecting leaks of the heating medium, since the flanges, bonnets and gland packings are potential leak points and need to be detected immediately in case of a leak. Naturally, if these are covered with insulation it will be very difficult to detect any leakage.
Be assured, that these uninsulated portions constitute a very small percentage of the total system surface area to be heated and any heat loss through the same can be practically neglected. However, if you still feel that this exercise needs to be done you can calculate the heat loss as per the method outlined in the above mentioned threads.
Happy calculating.
Regards,
Ankur.
#4
Posted 23 January 2009 - 06:05 AM
QUOTE (Qalander (Chem) @ Jan 23 2009, 11:41 AM) <{POST_SNAPBACK}>
QUOTE (WEEWA @ Jan 23 2009, 11:06 AM) <{POST_SNAPBACK}>
DEAR MY FRIEND
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
I NEED PROBLEM FOR HELP. MY PLANT TRIED TO MANAGE ENERGY CONSERVATION. AND I WANT TO CALCULATE HEAT LOSS AT FLANGE ,MANHOLE , VALVE , NOT HAVE INSULATION CAN YOU TELL ME ABOUT FORMULA TO CALCULATION HEAT LOSS.
THANK YOU VERY MUCH
Dear WEEWA Hello/ Good Morning,
Firstly avoid shouting at everyone else(stop use of Block Capitals)&clarify your background!
General heat transfer formula is Q=UXAXTemperature difference
"Q" is the Heat transfered,
"U" is the Heat transfer Coefficient for particular material invoved,
"A" is area available for(exposed to) heat transfer
"Temperature difference" between Inner(hotter) surface & 'Prevalent ambient(colder) temperatures'
Hope this helps
Qalander
#5
Posted 23 January 2009 - 06:23 AM
Dear Qalander,
You wanted to say something and seem to have forgotten.
Can I help you in any way.
Regards,
Ankur.
You wanted to say something and seem to have forgotten.
Can I help you in any way.
Regards,
Ankur.
#6
Posted 23 January 2009 - 09:41 AM
Weewa,
You can download one quite handy tool (3E Plus) and check the performance/heat losses of insulated and non-insulated systems:
http://www.pipeinsul...4/download.html
Just register yourself and download the package. It's a product of North American Insulation Manufacturers Association (NAIMA), and it is absolutely free of charge. Very user friendly, and with an option to expand the existing database with user-provided data.
You can download one quite handy tool (3E Plus) and check the performance/heat losses of insulated and non-insulated systems:
http://www.pipeinsul...4/download.html
Just register yourself and download the package. It's a product of North American Insulation Manufacturers Association (NAIMA), and it is absolutely free of charge. Very user friendly, and with an option to expand the existing database with user-provided data.
#7
Posted 23 January 2009 - 09:19 PM
QUOTE (Zauberberg @ Jan 23 2009, 07:41 PM) <{POST_SNAPBACK}>
Weewa,
You can download one quite handy tool (3E Plus) and check the performance/heat losses of insulated and non-insulated systems:
http://www.pipeinsul...4/download.html
Just register yourself and download the package. It's a product of North American Insulation Manufacturers Association (NAIMA), and it is absolutely free of charge. Very user friendly, and with an option to expand the existing database with user-provided data.
You can download one quite handy tool (3E Plus) and check the performance/heat losses of insulated and non-insulated systems:
http://www.pipeinsul...4/download.html
Just register yourself and download the package. It's a product of North American Insulation Manufacturers Association (NAIMA), and it is absolutely free of charge. Very user friendly, and with an option to expand the existing database with user-provided data.
Dear Friend Zauberberg, Thanks Very much indeed! for sharing useful info.
Best regards
Qalander
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |
||
Cross Over Temperature In Countercurrent Heat ExchangerStarted by Guest_panoska_* , 18 Feb 2025 |
|
![]() |
||
Aspen Hysys - Blowdown Utility Heat Flux MethodStarted by Guest_yuvi.ardekar1999@gmail.com_* , 27 Feb 2025 |
|
![]() |