Explosive Limits
#1 Guest_Kiran Parihar_*
  • guestGuests
Posted 17 September 2004 - 02:49 AM
I am facing a very interesting problem. I want to use Nitrogen for blanketting batch reactors of Ethylene Oxide.
As we all know, LEL & UEL of Ethylene Oxide in air is 3 - 100 % (v/v). I want to know if I can use 98.5 % (v/v) pure Nitrogen for this application (i.e 1.5 % Oxygen). What is the max. concentration of Oxygen that can be tolerated???
The discussions in the company threw up an interesting problem which I would like to state
What would be the effect on LEL & UEL for any gas if Air is deprived of Oxygen (i.e say 1.5 - 2 % Oxygen in air)
Or the air is enriched with Oxygen (i.e say 30 % & above Oxygen in air).
And how to determine the LEL & UEL under such circumstances.
#2 Diederik Zwart
Diederik Zwart
  • 21 posts
Posted 17 September 2004 - 07:25 AM
This topic was discussed previously:
I think you'll find what you're looking for if you go to: Limiting Oxygen Concentration
If the link doesn't work, do a search on "limiting" AND "oxygen", the topic was posted first on March 10 2003.
Good luck,
Diederik Zwart
#3 Guest_Kiran Parihar_*
  • guestGuests
Posted 17 September 2004 - 08:57 AM
Thanks Mr. Diederik Zwart for your response which will serve as a guidelines for Reactor Purging Systems.
Also I would like to know the estimation methods (if any) that are available for LEL & UEL under different Oxygen Concentrations.
Let us take an example of Benzene. LEL & UEL of Benzene, as we all know is 3.1 - 7.2 % v/v air. If suppose I increase the concentration of Oxygen, there should not be much change in LEL, but UEL will increase. How should this be estimated ???
#4 gvdlans
gvdlans
  • 619 posts
Posted 18 September 2004 - 08:19 AM
What you are looking for is the "flammability envelope" of your compound. If you draw a triangle with 100% flammable gas at the top corner, 100% oxygen at the lower lefthand corner and 100% nitrogen at the lower righthand corner. Inside this triangle (or tertiary diagram) you can draw a region inside this triangle where you have a flammable mixture. See figure 5 in the article found via following link (for hydrogen): Article with flammability envelope for hydrogen
You can construct the flammability envelope when you have literature data of flammable limits both in air and in pure oxygen. When plotting these upper and lower flammable limits in the tertiary diagram, and connecting the points by straight lines, you get a pretty good idea what the flammability envelope looks like. The figure 5 in above mentioned article is a good illustration of this method.
With this diagram you can find for any oxygen/nitrogen ratio what the flammability limits for your flammable gas are... Just draw a line from the top corner (with 100% flammable gas) to the point on the base line with the composition of your atmosphere (for example 30% oxygen, 70% nitrogen). Where this line crosses the flammability envelope you find the flammability limits. For most compounds you will find that for oxygen concentrations below about 10% (the limiting oxygen concentration) that the line does not cross the envelope. Here you really have an inert atmosphere...
See also NFPA 69 for more details.
#5 Guest_Guest_ramesh_*
  • guestGuests
Posted 21 September 2004 - 01:19 AM
i have seen the article on hydrogen.it shows safe zone for less than 4% oxygen.since you say mostly less than 10 % oxygen is safe,can we list out which all (there may be very few) gases may not be safe below 10% so that for all other gases we can sfely assume 10 % as the limit.
#6 gvdlans
gvdlans
  • 619 posts
Posted 21 September 2004 - 03:53 AM
Ramesh,
I strongly recommend you to get a copy of NFPA 69. It contains a good explanation on how to use the ternary diagram in Annex B, as well as a listing of Limiting Oxygen Concentrations (LOCs) in Annex C, both for N2/Air and for CO2/Air atmospheres. These LOCs were obtained at atmospheric temperature and pressure (so they are not valid at different process conditions..). For N2/Air atmospheres, the LOC for most gases is above 8%. but there are exceptions, for example:
Carbon Disulfide: 5.0%
Carbon Monoxide: 5.5%
Hydrogen: 5.0%
Dimethyl hydrazine: 7.0%
Note that this list in NFPA 69 is not complete, for example it does not contain ethylene oxide. So you cannot simply assume that LOC is above 8% just because it is not one of these four examples! It should also be noted that you should have a safety margin below this LOC. This is explained in chapter 5 of NFPA 69.
#7 Guest_Guest_ramesh_*
  • guestGuests
Posted 21 September 2004 - 05:25 AM
dear Jedi
thanks for info.i will certainly look into NFPA documents.